Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-UPS BX750MI report battery connect/disconnected mains connected/disconnected

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Back-UPS BX750MI report battery connect/disconnected mains connected/disconnected
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
mehari
mehari
Explorer

Posted: ‎2026-10-28 09:01 AM

0 Likes
6
162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-28 09:01 AM

Back-UPS BX750MI report battery connect/disconnected mains connected/disconnected

Hi,

I just got a new Back-UPS BX750MI and have it connected to a RaspberryPi using apcupsd.

The following is being reported when the mains is not plugged in

 

Oct 28 15:57:14 fw-test apcupsd[1044]: Mains returned. No longer on UPS batteries.
Oct 28 15:57:14 fw-test apcupsd[1044]: Power is back. UPS running on mains.
Oct 28 15:57:14 fw-test apcupsd[1044]: Power failure.
Oct 28 15:57:14 fw-test apcupsd[1044]: Battery disconnected.
Oct 28 15:57:20 fw-test apcupsd[1044]: Battery reattached.
Oct 28 15:57:20 fw-test apcupsd[1044]: Running on UPS batteries.

APC : 001,036,0892
DATE : 2026-10-28 16:00:16 +0000
HOSTNAME : fw-test
VERSION : 3.14.14 (31 May 2016) debian
UPSNAME : fw-test
CABLE : USB Cable
DRIVER : USB UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2026-10-28 15:47:15 +0000
MODEL : Back-UPS BX750MI
STATUS : SHUTTING DOWN
LINEV : 0.0 Volts
LOADPCT : 0.0 Percent
BCHARGE : 31.0 Percent
TIMELEFT : 20.5 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : Medium
LOTRANS : 145.0 Volts
HITRANS : 295.0 Volts
ALARMDEL : 30 Seconds
BATTV : 12.6 Volts
LASTXFER : Low line voltage
NUMXFERS : 6
XONBATT : 2026-10-28 15:59:22 +0000
TONBATT : 57 Seconds
CUMONBATT: 762 Seconds
XOFFBATT : 2026-10-28 15:59:21 +0000
SELFTEST : OK
STATFLAG : 0x05060210
SERIALNO : 9B2536A12148
BATTDATE : 2001-01-01
NOMINV : 230 Volts
NOMBATTV : 12.0 Volts
NOMPOWER : 410 Watts
END APC : 2026-10-28 16:00:19 +0000

Any idea if the UPS is faulty?

 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Teken
Champion

Posted: ‎2026-10-29 12:32 AM

0 Likes
0
160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-29 12:32 AM

Connect the unit to a computer running APC Power Chute (PCSS / PCPE) or NUT and report back the results. As it relates to Power Chute Software once the two systems are connected together complete the same (Lights Out / Grid Down) test and export the logs from PCSS and share the same here to the APC Forum for review:

 

https://www.se.com/ca/en/faqs/FA159672/

 

Questions Ask . . . đź‘Ť

Reply

Link copied. Please paste this link to share this article on your social media post.

mehari
mehari
Explorer

Posted: ‎2026-10-30 10:53 AM

0 Likes
0
132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-30 10:53 AM

I have replaced apcupsd with nut and I am not seeing the issue, the status I get is
battery.charge: 70
battery.charge.low: 10
battery.mfr.date: 2001/01/01
battery.runtime: 2747
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 13.3
battery.voltage.nominal: 12.0
device.mfr: American Power Conversion
device.model: Back-UPS BX750MI
device.serial: 9B2536A12148
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: auto
driver.state: updateinfo
driver.version: 2.8.1
driver.version.data: APC HID 0.100
driver.version.internal: 0.52
driver.version.usb: libusb-1.0.28 (API: 0x100010a)
input.sensitivity: medium
input.transfer.high: 295
input.transfer.low: 145
input.transfer.reason: input voltage out of range
input.voltage: 241.0
input.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.load: 0
ups.mfr: American Power Conversion
ups.mfr.date: 2025/09/03
ups.model: Back-UPS BX750MI
ups.productid: 0002
ups.realpower.nominal: 410
ups.serial: 9B2536A12148
ups.status: OL CHRG
ups.test.result: Done and passed
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d


so it looks like it is apcupsd's problem. I have used apcupsd on other APC UPS's and not had any issues.

 

Thanks for you suggestions and help.

Reply

Link copied. Please paste this link to share this article on your social media post.

mehari
mehari
Explorer

Posted: ‎2026-10-30 11:44 AM

0 Likes
1
132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-30 11:44 AM

I now see the same thing with NUT

Fri 30 Oct 18:39:01 GMT 2026
UPS fwtest@localhost battery is low
battery.charge: 82
battery.charge.low: 10
battery.mfr.date: 2001/01/01
battery.runtime: 3240
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 14.4
battery.voltage.nominal: 12.0
device.mfr: American Power Conversion
device.model: Back-UPS BX750MI
device.serial: 9B2536A12148
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: auto
driver.state: quiet
driver.version: 2.8.1
driver.version.data: APC HID 0.100
driver.version.internal: 0.52
driver.version.usb: libusb-1.0.28 (API: 0x100010a)
input.sensitivity: medium
input.transfer.high: 295
input.transfer.low: 145
input.transfer.reason: input voltage out of range
input.voltage: 241.0
input.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.load: 0
ups.mfr: American Power Conversion
ups.mfr.date: 2025/09/03
ups.model: Back-UPS BX750MI
ups.productid: 0002
ups.realpower.nominal: 410
ups.serial: 9B2536A12148
ups.status: OL DISCHRG LB RB
ups.test.result: Done and passed
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d

Fri 30 Oct 18:39:01 GMT 2026
UPS fwtest@localhost battery needs to be replaced
battery.charge: 82
battery.charge.low: 10
battery.mfr.date: 2001/01/01
battery.runtime: 3240
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 14.4
battery.voltage.nominal: 12.0
device.mfr: American Power Conversion
device.model: Back-UPS BX750MI
device.serial: 9B2536A12148
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: auto
driver.state: quiet
driver.version: 2.8.1
driver.version.data: APC HID 0.100
driver.version.internal: 0.52
driver.version.usb: libusb-1.0.28 (API: 0x100010a)
input.sensitivity: medium
input.transfer.high: 295
input.transfer.low: 145
input.transfer.reason: input voltage out of range
input.voltage: 241.0
input.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.load: 0
ups.mfr: American Power Conversion
ups.mfr.date: 2025/09/03
ups.model: Back-UPS BX750MI
ups.productid: 0002
ups.realpower.nominal: 410
ups.serial: 9B2536A12148
ups.status: OL DISCHRG LB RB
ups.test.result: Done and passed
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-11-03 05:25 AM

In response to mehari
0 Likes
0
129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-03 05:25 AM

You’ll need to provide the results using PCSS and share the logs for review:

 

https://www.se.com/us/en/faqs/FA159672/

Also, it’s unclear to me if the unit is operating correctly when AC Mains is present and connected - Yes / No?!?!

 

In the interim you may consider performing a brain dead reset (Twice) as outlined by this APC FAQ:

 

https://www.se.com/us/en/faqs/FA158947/

Lastly, confirm you’re using the supplied APC USB cable. Along with switching to another USB port to see if there is a change in behaviour.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

mehari
mehari
Explorer

Posted: ‎2026-11-04 08:16 AM

0 Likes
1
101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-04 08:16 AM

The unit is operating OK with mains connected, it operates as a UPS when mains disconnected but I get messages saying the battery needs replacing.

I ran it on battery for 40 mins and it discharged to around 40%, and the came back to 100% after several hours.

 

I haven't been able to find PCSS for arm linux (Raspbbery Pi) or Mac OSX (apple silicon) and I have no windows PCs.

 

When I can power of the connected equipment I will try the 'brain dead' procedure.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-11-05 09:22 AM

In response to mehari
0 Likes
0
96
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-05 09:22 AM

Power Chute PCSS does not support Arm Linux / Mac OSX. Regardless, the primary concern is whether the active fault is false flag vs real.

 

This is why its important to know what the system *Thinks* is currently the problem. In this case it thinks when the AC Mains is lost the RBC needs to be replaced.

 

Assuming you can't get a Windows computer to be connected to the system. The following action items would be used if available.

 

1. Brain Dead: Complete the brain dead reset twice. This will reset the unit to a factory state and clear any soft faults. A brain dead reset will not clear any hard faults such as a failed component / electrical fault.

 

2. Battery Install: Update the RBC installation date as doing so will reset internal counters and adjusts charging tables if applicable.

 

3. Self Test: Manually initiate a self test via (PCSS) as doing so will force the unit to perform a (POST) to detect the current state of health of the system. It will flag any (Active / Hard Faults) if present. The self test can also be invoked by pressing & holding down the power button.

 

4. Calibration: Manually initiate a battery calibration via (PCSS) with a minimum of 30% attached load or higher. Once complete allow the system to fully charge the RBC back to 100% SOC. This procedure will help teach the system the current state of health of the RBC.

 

NOTE: If the battery calibration can't be initiated by (PCSS) you may do so manually with similar results. Simply remove AC Mains from the wall outlet and let the system run down and shut off. Insure the unit is (NOT) connected to any sensitive electronics like a computer etc. or the system running NUT / APCUPSD. 

 

Once it shuts down reconnect AC Mains and let it fully charge back to 100%.

 

Questions Ask . . . đź‘Ť  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore