10 year old UPS began shutting down and restarting randomly today. No error messages and battery indicates fully charged. Line voltage is normal @ 118v.
Removed loads and took batteries out after manually shutting down and waited several minutes, replacing batteries and plugging BX1300G into a different outlet on a different circuit.
Within 2 - 3 minutes and with no load on UPS, it began again shutting down/restarting.
Ideas are welcome,
Thanks,
Doug
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-05-21 12:30 AM
It’s not clear to me based on your description that you replaced the RBC with new cells or simply completed a brain dead reset?!?
If the RBC was replaced with new cells then complete the following action items in sequence and report the outcome:
Brain Dead: Complete this task three times as outlined in this APC FAQ:
https://www.se.com/us/en/faqs/FA158947/
Date: Update the battery installation date via APC Power Chute Software. This will reset internal counters and adjust charging tables if applicable.
Self Test: Manually initiate a self test via Power Chute Software and allow the RBC to recover to 100% SOC (State of Charge). If the self test fails report that outcome here and call out any faults / codes declared by the system.
Calibration: Manually initiate a battery calibration via Power Chute Software with a minimum of 30% attached load or greater. Allow this process to complete and let the RBC recover to 100% SOC.
This will help the system learn the current RBC health and better reflect the operational runtime vis LCD, Power Chute.
NOTE: The RBC is designed to provide 2-5 years of service based on usage, temperature, and environmental conditions. The RBC is rated to provide 260 cycles subject to the same caveats.
The unit itself is designed with a useable service life of 8-10 years based on this APC FAQ:
https://www.se.com/us/en/faqs/FAQ000265093/
If you completed all the action items in sequence and the unit continues to misbehave. Then it’s time to replace the unit and purchase a new one.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-05-21 12:30 AM
It’s not clear to me based on your description that you replaced the RBC with new cells or simply completed a brain dead reset?!?
If the RBC was replaced with new cells then complete the following action items in sequence and report the outcome:
Brain Dead: Complete this task three times as outlined in this APC FAQ:
https://www.se.com/us/en/faqs/FA158947/
Date: Update the battery installation date via APC Power Chute Software. This will reset internal counters and adjust charging tables if applicable.
Self Test: Manually initiate a self test via Power Chute Software and allow the RBC to recover to 100% SOC (State of Charge). If the self test fails report that outcome here and call out any faults / codes declared by the system.
Calibration: Manually initiate a battery calibration via Power Chute Software with a minimum of 30% attached load or greater. Allow this process to complete and let the RBC recover to 100% SOC.
This will help the system learn the current RBC health and better reflect the operational runtime vis LCD, Power Chute.
NOTE: The RBC is designed to provide 2-5 years of service based on usage, temperature, and environmental conditions. The RBC is rated to provide 260 cycles subject to the same caveats.
The unit itself is designed with a useable service life of 8-10 years based on this APC FAQ:
https://www.se.com/us/en/faqs/FAQ000265093/
If you completed all the action items in sequence and the unit continues to misbehave. Then it’s time to replace the unit and purchase a new one.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-05-21 09:17 PM
Thanks for the road map and informative links. Following your insights, we have success!
As a note, the batteries are new (2025-04).
Appreciate the help,
Doug
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-05-22 03:39 AM
That’s great to hear and appreciate the quick feedback about the outcome.