Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BX1300G Randomly shuts down and restarts

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1300G Randomly shuts down and restarts
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Jeepdriver
Jeepdriver
Explorer

Posted: ‎2026-05-20 04:04 PM

0 Likes
3
212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-20 04:04 PM

BX1300G Randomly shuts down and restarts

10 year old UPS began shutting down and restarting randomly today. No error messages and battery indicates fully charged. Line voltage is normal @ 118v.

 

Removed loads and took batteries out after manually shutting down and waited several minutes, replacing batteries and plugging BX1300G into a different outlet on a different circuit.

 

Within 2 - 3 minutes and with no load on UPS, it began again shutting down/restarting.

 

Ideas are welcome,

Thanks,

Doug

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2026-05-21 12:30 AM

0 Likes
0
207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-21 12:30 AM

It’s not clear to me based on your description that you replaced the RBC with new cells or simply completed a brain dead reset?!?

 

If the RBC was replaced with new cells then complete the following action items in sequence and report the outcome:

 

Brain Dead: Complete this task three times as outlined in this APC FAQ:

 

https://www.se.com/us/en/faqs/FA158947/

 

Date: Update the battery installation date via APC Power Chute Software. This will reset internal counters and adjust charging tables if applicable.

 

Self Test: Manually initiate a self test via Power Chute Software and allow the RBC to recover to 100% SOC (State of Charge). If the self test fails report that outcome here and call out any faults / codes declared by the system.

 

Calibration: Manually initiate a battery calibration via Power Chute Software with a minimum of 30% attached load or greater. Allow this process to complete and let the RBC recover to 100% SOC.

 

This will help the system learn the current RBC health and better reflect the operational runtime vis LCD, Power Chute.

 

NOTE: The RBC is designed to provide 2-5 years of service based on usage, temperature, and environmental conditions. The RBC is rated to provide 260 cycles subject to the same caveats.

 

The unit itself is designed with a useable service life of 8-10 years based on this APC FAQ:

 

 https://www.se.com/us/en/faqs/FAQ000265093/

 

If you completed all the action items in sequence and the unit continues to misbehave. Then it’s time to replace the unit and purchase a new one.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Teken
Champion

Posted: ‎2026-05-21 12:30 AM

0 Likes
0
208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-21 12:30 AM

It’s not clear to me based on your description that you replaced the RBC with new cells or simply completed a brain dead reset?!?

 

If the RBC was replaced with new cells then complete the following action items in sequence and report the outcome:

 

Brain Dead: Complete this task three times as outlined in this APC FAQ:

 

https://www.se.com/us/en/faqs/FA158947/

 

Date: Update the battery installation date via APC Power Chute Software. This will reset internal counters and adjust charging tables if applicable.

 

Self Test: Manually initiate a self test via Power Chute Software and allow the RBC to recover to 100% SOC (State of Charge). If the self test fails report that outcome here and call out any faults / codes declared by the system.

 

Calibration: Manually initiate a battery calibration via Power Chute Software with a minimum of 30% attached load or greater. Allow this process to complete and let the RBC recover to 100% SOC.

 

This will help the system learn the current RBC health and better reflect the operational runtime vis LCD, Power Chute.

 

NOTE: The RBC is designed to provide 2-5 years of service based on usage, temperature, and environmental conditions. The RBC is rated to provide 260 cycles subject to the same caveats.

 

The unit itself is designed with a useable service life of 8-10 years based on this APC FAQ:

 

 https://www.se.com/us/en/faqs/FAQ000265093/

 

If you completed all the action items in sequence and the unit continues to misbehave. Then it’s time to replace the unit and purchase a new one.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Jeepdriver
Jeepdriver
Explorer

Posted: ‎2026-05-21 09:17 PM

0 Likes
1
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-21 09:17 PM

Thanks for the road map and informative links. Following your insights, we have success!

As a note, the batteries are new (2025-04).

 

Appreciate the help,

Doug

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-05-22 03:39 AM

In response to Jeepdriver
0 Likes
0
176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-22 03:39 AM

That’s great to hear and appreciate the quick feedback about the outcome.

 

Rock On . . . 🤘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore