Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

BR1300LCD How to disassemble the case?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: BR1300LCD How to disassemble the case?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
JeffLiebermann_apc
Crewman JeffLiebermann_apc
Crewman

Posted: ‎2021-06-29 07:31 PM

0 Likes
2
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 07:31 PM

BR1300LCD How to disassemble the case?

This was originally posted on APC forums on 1/3/2013


One of my customers has several APC BR1300LCD UPS's. All but one are working fine. It erratically refuses to charge the battery. Eventually, the display shows a totally discharged battery. I've replaced both batteries twice, without effect. The problem comes and goes, which suggests a loose terminal. It's time to dive inside the guts and fix it but I'm having problems opening the case. I've removed 4 screws from the back, and two screws inside the battery compartment. The back panel comes off. The front panel refuses to release. How do I get the front panel off and how to I get access to the PCB?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • disassemble
  • repair
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffLiebermann_apc
Crewman JeffLiebermann_apc
Crewman

Posted: ‎2021-07-05 07:12 PM . Last Modified: ‎2021-07-05 07:15 PM

In response to BillP
0 Likes
0
320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-05 07:12 PM . Last Modified: ‎2021-07-05 07:15 PM

Amazing.  8.5 years later and I finally see some interest in the problem.

 

I was eventually able to disassemble the case and fix the problem.  See photos at:
http://www.learnbydestroying.com/jeffl/pics/repair/APC%20XS-1300/index.html

I don't recall exactly what I did to disassemble the case, but the photos should help.  The basic idea is to remove the screws and locking tabs as shown by the red circles and red arrows.  I have two or three of these also in need of repair that I can take apart and make some better photos if anyone is interested.

 

The failure to charge the batteries was caused by a defective 22uf 400v electrolytic capacitor (C69) as shown at:

http://www.learnbydestroying.com/jeffl/pics/repair/APC%20XS-1300/index.html#XS-1300-03.jpg 

I didn't have an exact replacement capacitor handy, so the capacitor on the PCB is in a smaller package. 

 

In the past 8.5 years, I've repaired about 10 APC XS-1300 UPS's by replacing C69.  Unfortunately, the initial 3 UPS's came back with the same charging problem and the same bulging capacitor problem.  Apparently, my replacement capacitor was no better than the original failed capacitor.  I don't recall exactly what capacitor eventually worked, but I did recall it came from Panasonic.  I can dig out the details if anyone is interested.

 

The failure to charge problem is rather irritating because most of my customers assumed that the battery had died and purchased replacement batteries, which did the same thing and refused to charge.  Actually, both the original and the replacement batteries died rather rapidly because gel-cell and AGM batteries don't like to remain in the discharged state for very long.

 

I do not believe that the problem is caused by a defective capacitor.  Rather, I believe it might be a design problem where there is too much ripple current going through the capacitor causing it to get hot and shorten its useful life.  I haven't done anything to investigate this possibility so please consider this pure speculation.  If I had a schematic, I would probably make whatever changes are necessary to reduce the ripple current.  I'll spare you my rant about manufacturers who fail to supply repair information and replacement parts.

 

 

 

See Answer In Context

  • Tags:
  • english
Reply
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:31 PM

0 Likes
1
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 07:31 PM

This reply was originally posted by Chris on APC forums on 1/4/2013


This is of course something APC can't help you with, but anyone else with any ideas for Jeff?

Reply
JeffLiebermann_apc
Crewman JeffLiebermann_apc
Crewman

Posted: ‎2021-07-05 07:12 PM . Last Modified: ‎2021-07-05 07:15 PM

In response to BillP
0 Likes
0
321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-05 07:12 PM . Last Modified: ‎2021-07-05 07:15 PM

Amazing.  8.5 years later and I finally see some interest in the problem.

 

I was eventually able to disassemble the case and fix the problem.  See photos at:
http://www.learnbydestroying.com/jeffl/pics/repair/APC%20XS-1300/index.html

I don't recall exactly what I did to disassemble the case, but the photos should help.  The basic idea is to remove the screws and locking tabs as shown by the red circles and red arrows.  I have two or three of these also in need of repair that I can take apart and make some better photos if anyone is interested.

 

The failure to charge the batteries was caused by a defective 22uf 400v electrolytic capacitor (C69) as shown at:

http://www.learnbydestroying.com/jeffl/pics/repair/APC%20XS-1300/index.html#XS-1300-03.jpg 

I didn't have an exact replacement capacitor handy, so the capacitor on the PCB is in a smaller package. 

 

In the past 8.5 years, I've repaired about 10 APC XS-1300 UPS's by replacing C69.  Unfortunately, the initial 3 UPS's came back with the same charging problem and the same bulging capacitor problem.  Apparently, my replacement capacitor was no better than the original failed capacitor.  I don't recall exactly what capacitor eventually worked, but I did recall it came from Panasonic.  I can dig out the details if anyone is interested.

 

The failure to charge problem is rather irritating because most of my customers assumed that the battery had died and purchased replacement batteries, which did the same thing and refused to charge.  Actually, both the original and the replacement batteries died rather rapidly because gel-cell and AGM batteries don't like to remain in the discharged state for very long.

 

I do not believe that the problem is caused by a defective capacitor.  Rather, I believe it might be a design problem where there is too much ripple current going through the capacitor causing it to get hot and shorten its useful life.  I haven't done anything to investigate this possibility so please consider this pure speculation.  If I had a schematic, I would probably make whatever changes are necessary to reduce the ripple current.  I'll spare you my rant about manufacturers who fail to supply repair information and replacement parts.

 

 

 

  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc