Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BN1500M2 Power dropping.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: BN1500M2 Power dropping.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
yoyodyne2112
yoyodyne2112
Explorer

Posted: ‎2026-08-20 08:29 PM

0 Likes
5
199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-20 08:29 PM

BN1500M2 Power dropping.

APC Back-UPS 1500 (BN1500M2) provides surge and backup power for a home office, connected devices include a Macbook Pro, CalDigit hub, a pair of SONY Bravia 40" monitors, an internet modem, and gateway.  Power has dropped twice today.  The duration of each drop was less than one second, resulting in the monitors resetting (simple power off/on event) and Macbook pausing (no reset, just pause).

There were no other indications of a power issue in the house, no lights dimming/flickering, and no warning tones from the UPS indicating a power loss.  The only outward indication of any issue was the monitor reset.  The UPS display is typical, when queried it indicates a 150W load, 121V @ 60Hz, but shows 19 events logged since installation roughly 2.5 years ago.  Unfortunately, it has been a while since I had a concern that necessitated checking the event log, so I have no idea whether the issues experienced today were logged.

We are located on the island of Hawai'i and operate on 100% solar power.  The system is about 18 months old, and we do not rely on grid service, except for when the weather is such that the system is unable to keep up with demand.  The recent hurricane activity (hurricane Lala) did just that, but we experienced no issues switching from solar power to grid power and back to solar before the storm to fully charge our storage batteries, and we expect to go through this again soon, as another storm is approaching the islands.

 

I have cleared the event log and will be tracking activity daily, to see if there is an outside influenence causing these drops, but don't feel like that is even remotely possible given the fact that the only devices affected are connected to the BN1500 only.  I would like to know whether anyone else has experienced something of this nature, momentary power loss to connected devices, without audible warnings, and with no other parallel issues in household lighting, etc.

Thanks in advance for any advice,

 

Mike

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Home & Office - UPS & Software
  • Tags:
  • english
  • freaky
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2026-08-21 04:59 AM

0 Likes
4
195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-21 04:59 AM

At first blush I would say the UPS transfer time isn’t fast enough for the hardware in place. You can easily prove two things right now.

 

Transfer time and RBC health by removing AC Mains from the wall outlet. If you see the same behaviour simply by removing AC power from the wall outlet.

 

The transfer time is too long and the only solution is to live with the problem or replace the unit with better specifications. If during the tests you also see the unit turn off immediately or far below the expected operational runtime when compared to the APC Online Runtime Calculator than the RBC is near end of life and needs to be replaced.

 


Given the information you provided the RBC and unit are still under warranty. As such (IF) the validation tests show a bad RBC have it replaced under warranty.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Teken
Teken
Champion

Posted: ‎2026-08-21 04:59 AM

0 Likes
4
196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-21 04:59 AM

At first blush I would say the UPS transfer time isn’t fast enough for the hardware in place. You can easily prove two things right now.

 

Transfer time and RBC health by removing AC Mains from the wall outlet. If you see the same behaviour simply by removing AC power from the wall outlet.

 

The transfer time is too long and the only solution is to live with the problem or replace the unit with better specifications. If during the tests you also see the unit turn off immediately or far below the expected operational runtime when compared to the APC Online Runtime Calculator than the RBC is near end of life and needs to be replaced.

 


Given the information you provided the RBC and unit are still under warranty. As such (IF) the validation tests show a bad RBC have it replaced under warranty.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

yoyodyne2112
yoyodyne2112
Explorer

Posted: ‎2026-08-21 01:33 PM

In response to Teken
0 Likes
3
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-21 01:33 PM

Thanks for your response and the information you provided.  Prior to reading your message, I experienced another incident and since I was not surprised by the event I was able to notice more of the device behaviors specific to the event. The monitors are not powering down as previously thought, the HDMI input signal to the monitors is glitching, but I will proceed with the testing you advised, to confirm.

...................

I just completed the test you advised, and the unit is functioning properly: switching was automatic when the AC input was disconnected, the event logged correctly, and there was no disruption to the video signal or power to the monitors. 

With that in mind, the next link in the chain of equipment affecting both monitors would be the CalDigit hub.

 

Thanks again,

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-08-25 04:39 AM

In response to yoyodyne2112
0 Likes
2
141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-25 04:39 AM

Keep us updated as to the final outcome and what you find. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

yoyodyne2112
yoyodyne2112
Explorer

Posted: ‎2026-08-26 08:05 PM

In response to Teken
0 Likes
1
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-26 08:05 PM

Thanks again, for your advice.

I have been able to confirm that the BN1500M2 is not the issue, it is performing fine.  The issue turned out to be a needed firmware update for the CalDigit hub.  I was able to isolate the issue to the hub after a couple days of monitoring, and once I was able to confirm it was the culprit, I confirmed that an upgraded firmware was available and that took care of the issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-08-27 05:04 AM

In response to yoyodyne2112
0 Likes
0
111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-27 05:04 AM

Hi Mike,

 

Appreciate the follow up and identifying root cause and the final solution.

 

Rock On . . . 🤘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore