Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

BE750G: powerchute says "remaining battery charge is 101%, battery is currently charging" what is going on?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: BE750G: powerchute says "remaining battery charge is 101%, battery is currently charging" what is going on?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
daaan_apc
Ensign daaan_apc
Ensign

Posted: ‎2021-06-29 09:29 PM

0 Likes
12
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

BE750G: powerchute says "remaining battery charge is 101%, battery is currently charging" what is going on?

This was originally posted on APC forums on 1/5/2014


i just purchased a BE750G the other day. i noticed that half the time i look, powerchute personal edition 3.0.2 says "remaining battery charge is 101%, battery is currently charging". the rest of the time, everything is fine. is something wrong with my unit or battery?

2104_101 percent.jpg

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • be750g
  • question
  • ups
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:30 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:30 PM

This reply was originally posted by Angela on APC forums on 11/20/2015


Hello,

Unfortunately the user cannot apply this firmware update for this specific UPS model (or most Back-UPS products). If this is bothersome, you'll have to contact tech support for an RMA to replace the entire UPS.

See Answer In Context

Reply
Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This reply was originally posted by Angela on APC forums on 1/6/2014


From my research, it looks like a bug on the UPS firmware side.

Under About under help and support in PowerChute, what is the UPS firmware version? It appears to be very random and what I'd suggest is to perhaps try resetting the UPS and see if it goes away. To reset it, turn off and unplug any attached devices, including the USB cable. Turn the UPS itself off and unplug it from AC power. Disconnect and remove the battery and hold down the power button for about 15 seconds. Reconnect the battery. Reconnect the UPS to AC power and turn it on. Reconnect your attached devices and USB cable and you can then turn them on and re-check PowerChute.

Reply
daaan_apc
Ensign daaan_apc
Ensign

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This was originally posted on APC forums on 1/6/2014


the firmware version is 908.W3.D

Reply
daaan_apc
Ensign daaan_apc
Ensign

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This was originally posted on APC forums on 1/6/2014


angela, i followed your instructions but the problem still persists.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This reply was originally posted by Angela on APC forums on 1/8/2014


Working on it - let me see what our end game will be. smile I'll report back ASAP.

Reply
daaan_apc
Ensign daaan_apc
Ensign

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This was originally posted on APC forums on 1/10/2014


thanks for the info.  will i be able to upgrade the firmware in my unit when the new version is released? or am i stuck with the bug?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This reply was originally posted by Angela on APC forums on 1/10/2014


I have confirmed this is a cosmetic only firmware bug that will be addressed next month in new units. If you see 101% and charging, it does indicate the UPS is really at 100% and fully charged.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This reply was originally posted by Angela on APC forums on 1/10/2014


This unit is not technically firmware upgradable for this UPS by a user but when the firmware is available, we can discuss options if you don't want to live with this.

Reply
daaan_apc
Ensign daaan_apc
Ensign

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This was originally posted on APC forums on 1/10/2014


i would like to discuss those options.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:29 PM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:29 PM

This reply was originally posted by Angela on APC forums on 1/10/2014


Well I guess I meant more when it is confirmed there is a fix available since I can't do anything right this second unfortunately. I was told next month this would be in production so when it is, I can circle back with you. Feel free to post for an update if you don't hear from me.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:30 PM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:30 PM

This reply was originally posted by Angela on APC forums on 12/19/2014


Hello - FYI - this issue is resolved in BE750G firmware W4 (where you had firmware W3). 

Reply
nigeltufnelny_apc
nigeltufnelny_apc
Cadet

Posted: ‎2021-06-29 09:30 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:30 PM

This was originally posted on APC forums on 11/20/2015


Hello, I just bought an ES-750 and am also seeing the 101% problem.  I have W3.  Where can I get W4?  Thanks.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:30 PM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:30 PM

This reply was originally posted by Angela on APC forums on 11/20/2015


Hello,

Unfortunately the user cannot apply this firmware update for this specific UPS model (or most Back-UPS products). If this is bothersome, you'll have to contact tech support for an RMA to replace the entire UPS.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc