Are APC products suitable for Audiophile equipment support

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Are APC products suitable for Audiophile equipment support
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
5
5287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

Are APC products suitable for Audiophile equipment support

I use dozens of APC UPS's in my computer support business, but am not an EE.

I've had great stereo equipment for years, but just recently started to learn more in a couple of high-end audio forums.

I've always assumed clean power is clean power, and felt a properly sized APC would condition power to an audio amplifier, turntable or CD player just as well as to a PC. A lot of snobs in these groups seem to feel APC is NOT "audiophile" grade.

Is there any reason the collection of components (capacitors, resistors, transistors, etc.) in APC would not be as good at providing power as those brands claiming to be "audio power conditiioners"?

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • audio
  • audiophile
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

Thanks, that clears up my questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

I understand many amplifiers can present extremely complex high-current loads to the electrical circuit. I'm guessing even a relatively robust computer UPS like an old Back-UPS Pro 1100 would not be suitable.

But for a CD player or turntable, I would think even a 350 and certainly 550, 650, 725 models would suffice unless there si some specific difference with the circuitry that would affect audio properties.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

The BE series 350, 550s, etc. pass utility power to the load while the UPS senses that power input is acceptable, and during this time there is nothing in the UPS circuitry that would cause issues with a device such as a CD player. When the Back-UPS series goes to battery they create a stepped-approximated sine wave that can cause sensitive electronic equipment or devices with Power Factor Corrected power supplies to skip or reboot, but if this is just a portable CD player or "boombox" it should be just fine.

I would keep high-end AV equipment away from the Back-UPS series and move towards our AV line of products. If you are restricted by price...you could get away with a Smart-UPS since they are a higher performing brand of UPS (in terms of on battery output, voltage regulation, state transfer times, monitoring, etc.), although they are much less feature "rich" in terms of AV functionality.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 5
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

Thanks, that clears up my questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

[take a look at our audio/video products here|http://www.apc.com/products/category.cfm?id=15]

those are the products i'd have to recommend for audio video equipment. these products are built to filter noise and sustain themselves under high current situations which a lot of audio video equipment present when they turn on. their internal components are rated to do the job and are advertised to do so.

a regular UPS probably wouldnt handle a high current draw/really fast overload as well as these devices would.

did you have a specific model you were talking about though? that isnt in the AV line up?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

inspired wrote:
I use dozens of APC UPS's in my computer support business, but am not an EE.

I've had great stereo equipment for years, but just recently started to learn more in a couple of high-end audio forums.

I've always assumed clean power is clean power, and felt a properly sized APC would condition power to an audio amplifier, turntable or CD player just as well as to a PC. A lot of snobs in these groups seem to feel APC is NOT "audiophile" grade.

Is there any reason the collection of components (capacitors, resistors, transistors, etc.) in APC would not be as good at providing power as those brands claiming to be "audio power conditiioners"?
Clean power is indeed clean power. There's no real difference between one conditioner that outputs 120v @ 60hz and another unit from another mfg. that has the same output (assuming neither unit has a fault on it), other than potentially having input line "noise" passed along to the load, or allowing feedback or "signals" passed between the load components.

Our APC AV power conditioners and UPS systems have isolated, filtered sets of outlets that are meant to provide the cleanest power possible to the attached load and prevent the passage of signals/transients from one outlet to another. We use high quality MOVs and other surge protection circuitry to allow our power conditioners and UPS systems to have a "let through voltage" that is above and beyond the UL standard for let through/clamp voltages. Our power conditioners/UPS' also have active EMI/RFI noise filtering, and are designed for systems that have high inrush currents such as amps, speakers and subwoofers, and we also provide delayed outlets for such systems to prevent overload or power up in stages to prevent transient feedback or signals between connected components. Our AV power conditioners and UPS' also have Automatic Voltage Regulation through a tap transformer built into the UPS' output, which allows us to "boost or trim" bad voltage to ensure steady output to the load. We also provide a high quality, gold plated AV coax cable to use with the unit (on most AV offerings).

Does APC make the best AV power conditioners? I'm sure some would disagree...but then again there are a lof of people that claim Monster HDMI and AV cables are light years better than regular cables, and there's mountains of evidence against that ๐Ÿ˜›

You can check out our product offerings here:
http://www.apc.com/products/category.cfm?id=15

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

I understand many amplifiers can present extremely complex high-current loads to the electrical circuit. I'm guessing even a relatively robust computer UPS like an old Back-UPS Pro 1100 would not be suitable.

But for a CD player or turntable, I would think even a 350 and certainly 550, 650, 725 models would suffice unless there si some specific difference with the circuitry that would affect audio properties.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

0 Likes
0
5288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:43 PM . Last Modified: โ€Ž2024-03-21 02:33 AM

The BE series 350, 550s, etc. pass utility power to the load while the UPS senses that power input is acceptable, and during this time there is nothing in the UPS circuitry that would cause issues with a device such as a CD player. When the Back-UPS series goes to battery they create a stepped-approximated sine wave that can cause sensitive electronic equipment or devices with Power Factor Corrected power supplies to skip or reboot, but if this is just a portable CD player or "boombox" it should be just fine.

I would keep high-end AV equipment away from the Back-UPS series and move towards our AV line of products. If you are restricted by price...you could get away with a Smart-UPS since they are a higher performing brand of UPS (in terms of on battery output, voltage regulation, state transfer times, monitoring, etc.), although they are much less feature "rich" in terms of AV functionality.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of