We Value Your Feedback! Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services. Learn more about the survey or Click here to Launch the survey Schneider Electric Services Innovation Team!
Apc selection and inrush current
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-0906:16 AM
If this message / indicator is showing this means there’s a problem with the connected load. More than likely the unit is simply overloaded and thus shutting down.
You can test this theory by simply replacing the load with something else and see how the unit behaves and report back the results.
Generally speaking a UPS should only be loaded up to 80% of it’s rated capacity. A 700 RMS load should have at least 1000 ~ 1500 VA UPS at the lower tier.
A 2000 VA is more appropriate in terms of capacity, headroom, and operational runtime to complete a graceful shutdown.
Questions Ask . . . 👍
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.