Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Apc Backup pro 1000 running on battery when apartment generator power is on

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Apc Backup pro 1000 running on battery when apartment generator power is on
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
kaustubh123_apc
Crewman kaustubh123_apc
Crewman

Posted: ‎2021-06-29 09:41 PM

0 Likes
5
421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:41 PM

Apc Backup pro 1000 running on battery when apartment generator power is on

This was originally posted on APC forums on 3/18/2014


Hi I have a apc backup pro 1000 connected to my computer for backup. The apartment complex I live in has a power generator but my apc ups switches to using battery when the generator is active. The input voltage on the ups display is 217-218 volts at 47 hz when the generator is active. I have tried switching the ups sensitivity to low but it still run on battery. Can someone please explain why when everything in cluding my tv and fridge run normally  when the generator is active but the ups switches to using its reserve battery instead.

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • battery
  • power
  • question
  • ups
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:41 PM

0 Likes
0
421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:41 PM

This reply was originally posted by Joe on APC forums on 3/19/2014


Specialized test equipment, such as a power line monitor, would be able to detect such distortion if present.  I am not sure about your specific UPS, but most of them have the ability to create an event log that may be able to capture the reason that it continues to remain on battery power.

I am assuming that the generator in your building takes at least several seconds to pick up the load after a power failure and total loss of power is the reason that your UPS kicks in.  It may be possible to restart your UPS during the time the building is on emergency power and then check the event log for possible reasons it refuses to transition to building AC power.

See Answer In Context

Reply
Replies 5
Battman_apc
Commander Battman_apc
Commander

Posted: ‎2021-06-29 09:41 PM

0 Likes
0
422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:41 PM

This was originally posted on APC forums on 3/18/2014


Hello, from your profile it appears you are located in India - but it would help to know for your exact area what normal voltage and frequency of the power in your building ? Thanks.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:41 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:41 PM

This reply was originally posted by Joe on APC forums on 3/19/2014


Although the generator may be indicating appropriate output voltage level and frequency, other aspects of the waveform itself, such as heavy distortion, etc, would still be unacceptable to the UPS which would continue to remain on battery.

Reply
kaustubh123_apc
Crewman kaustubh123_apc
Crewman

Posted: ‎2021-06-29 09:41 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:41 PM

This was originally posted on APC forums on 3/19/2014


Hi , yes I am in the banglore city in india and the normal power voltage is 238-240 volts at 50 hz. Currently my building is running on the generator for the past 14 hours due to a fault in the main electical line. Since my ups troes to run on the battery for when the generator is active it has shut down a couple of imes but if I turn it on after a few hours later the battery is fully charged again. So it is receving charge when on the generator power but still uses the battery when turned on

Reply
kaustubh123_apc
Crewman kaustubh123_apc
Crewman

Posted: ‎2021-06-29 09:41 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:41 PM

This was originally posted on APC forums on 3/19/2014


Hi if it is the waveform distortion distortion causing the ups to use its battery is there a way to detect such a issue. Currently as I stated in the op all other equipment in the house including the fridge and tv seem to be operating normally on the generator power but the ups does not . The power and frequency inputs which display on the ups also do not vary over time. So the generator power seems to be stable at 217-218 volts at 47hz.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:41 PM

0 Likes
0
422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 09:41 PM

This reply was originally posted by Joe on APC forums on 3/19/2014


Specialized test equipment, such as a power line monitor, would be able to detect such distortion if present.  I am not sure about your specific UPS, but most of them have the ability to create an event log that may be able to capture the reason that it continues to remain on battery power.

I am assuming that the generator in your building takes at least several seconds to pick up the load after a power failure and total loss of power is the reason that your UPS kicks in.  It may be possible to restart your UPS during the time the building is on emergency power and then check the event log for possible reasons it refuses to transition to building AC power.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc