Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

APS Back-UPS ES 700 Continuous Tone

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: APS Back-UPS ES 700 Continuous Tone
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
HenleyBranch_apc
HenleyBranch_apc
Cadet

Posted: ‎2021-06-28 04:29 AM

0 Likes
7
9258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 04:29 AM

APS Back-UPS ES 700 Continuous Tone

This was originally posted on APC forums on 4/5/2016


Hi there, 

We have a couple of APS Back-UPS units on site, and one suddenly started producing a continuous tone. Reading from a previous thread, I have replaced the battery and it is continuing to do the same thing (annoying after buying a replacement battery). The unit is three years old. 

Model: BE700G-UK Serial: 5B1241T04332

To answer the diagnosis questions in that thread: 

* On the said occasion wherein the UPS produced the constant tone, did the system block and monitor turned off? How about the load that are attached on the Surge only side?

No power from any outlets. 

* Have you ever noticed that the circuit breaker near the input plug of the unit was popped out while the UPS was on that state?

Circuit breaker is in, and hasn't popped out. 


* With the UPS attached to the wall outlet/ power source and the regular load are connected to the unit I would like you to unplug the UPS from the power source and let me know what will happen.

Continuous high-pitched tone continues when disconnected. Power LED is off. 


* Is the UPS making any type of noise?

When power button is pressed, power LED blinks briefly, there is a brief 'scratching' noise from inside the unit (sounds like relays?), then the power LED goes out and the continuous high-pitched tone continues. Pressing and holding power button causes the noise to sop, turns unit off. 

   
* The LED next to the power switch, was it blinking or solid? If it is, what color was the LED?

As above, LED was green briefly then goes out and continuous tone sounds.

 
* Make sure as well that the battery is properly attached to the unit. Check if there's any noticeable damage to the battery, see if there is any crack or acid coming out from the battery.

Double-checked connections. As noted above, battery has been replaced. 

What does the continuous tone mean?

HB

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • es700
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:29 AM

0 Likes
2
9239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 04:29 AM

This reply was originally posted by Bill on APC forums on 4/6/2016


Hi,

Reset the UPS and if that does not resolve the issue then the UPS should be replaced.

To reset follow the below procedure;
 

1: Disconnect any attached load.

2: Unplug the UPS from the wall socket.

3: Disconnect the UPS' internal battery.

4: Push and hold the "On" button on the UPS for 5 seconds

5: Reconnect internal battery.

6: Plug UPS in to known good power source.

7: Turn UPS on.

See Answer In Context

Reply
Share
surdu_apc
Crewman surdu_apc
Crewman

Posted: ‎2021-06-28 04:29 AM

0 Likes
0
9239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 04:29 AM

This was originally posted on APC forums on 2/3/2020


Sorry for the late response, but hopefully it will help someone else.

I had the same issue. I wrote a blog post on how I fixed it here: https://surdu.me/2019/09/03/fix-apc-es700-constant-beeping.html

See Answer In Context

Reply
Share
Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:29 AM

0 Likes
2
9240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 04:29 AM

This reply was originally posted by Bill on APC forums on 4/6/2016


Hi,

Reset the UPS and if that does not resolve the issue then the UPS should be replaced.

To reset follow the below procedure;
 

1: Disconnect any attached load.

2: Unplug the UPS from the wall socket.

3: Disconnect the UPS' internal battery.

4: Push and hold the "On" button on the UPS for 5 seconds

5: Reconnect internal battery.

6: Plug UPS in to known good power source.

7: Turn UPS on.

Reply
Share
surdu_apc
Crewman surdu_apc
Crewman

Posted: ‎2021-06-28 04:29 AM

0 Likes
0
9240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 04:29 AM

This was originally posted on APC forums on 2/3/2020


Sorry for the late response, but hopefully it will help someone else.

I had the same issue. I wrote a blog post on how I fixed it here: https://surdu.me/2019/09/03/fix-apc-es700-constant-beeping.html

Reply
Share
Geo
Geo
Cadet

Posted: ‎2022-01-22 02:52 AM

In response to BillP
0 Likes
1
8844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-01-22 02:52 AM

I'm sorry but I'm very disappointed by this UPS.

I have the same problem and the "reset" didn't do anything. Same continuous beep and no power given to any socket.

This is ridiculous, from all points of view. Business strategy, quality of service, eco-awareness etc - you name it.

 

Here's why:

I paid (not cheapest price) for a tool (APC) to protect my important electric devices.

The tool died after 2 years or so (as you confirm that "the UPS should be replaced") and I am pretty sure contributed to frying my computer's motherboard.

This "Uninterrupted" power supply not only did not ensure power to my expensive computer but in fact *INTERRUPTED* power by itself without any power failure from the wall socket, forcing my machine to go into a forced hard reset.

Therefore, we conclude that once the UPS becomes a "faulty UPS" for whatever internal circuit reason - it also becomes a computer/motherboard frying solution.

I will write a blog - how to fry a motherboard by using a UPS.

 

Furthermore, once the owner is aware that the UPS can destroy devices - s/he is stuck with a (very likely) not recyclable black thing that cannot be used even as a bulky power extension with some sort of surge protection at least - which would have avoided killing my motherboard.

 

Whoever is in charge with designing these UPS's should rethink everything from scratch.

The UPS functions on the premise that *only* the power source can be *ever* at fault - and not itself, which is clearly not the case.

These UPS's *MUST* have a compulsory fail-over solution for its own faults, by allowing power source to reach devices, while informing the owner (beeping, flashing whatever). But don't cut the power to my machine. Just don't.

 

  • Tags:
  • english
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-02-01 07:11 AM

In response to Geo
0 Likes
0
8730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-02-01 07:11 AM

@Geo 

 

Sorry to hear of your inconvenience. The UPS has a lifetime equipment protection policy. You should contact local support for assistance. 

 

Local support contact information will be found at this link.

https://www.apc.com/us/en/support/contact-us/index.jsp

You may need to change the region in the upper left of the contact us web page. 

 

  • Tags:
  • english
Reply
Share
andreiox
andreiox
Cadet

Posted: ‎2022-05-16 11:54 PM

0 Likes
2
7712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-05-16 11:54 PM

Hello, the link (https://surdu.me/2019/09/03/fix-apc-es700-constant-beeping.html) is not working any more!

  • Tags:
  • english
Reply
Share
Chris.scotland
Chris.scotland
Cadet

Posted: ‎2022-09-05 10:30 AM

In response to andreiox
0 Likes
1
5704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-09-05 10:30 AM

The internet archive has a copy of this page: https://web.archive.org/web/20210514033853/https://surdu.me/2019/09/03/fix-apc-es700-constant-beepin...

 

For anyone else basically the issue for this guy was some blown capacitors on the main circuit board.

  • Tags:
  • english
Reply
Share
Chris.scotland
Chris.scotland
Cadet

Posted: ‎2022-09-07 02:54 PM

In response to Chris.scotland
0 Likes
0
5616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-09-07 02:54 PM

For future reference and in case it is helpful to others I also experienced a random shutdown of my UPS accompanied by a continuous tone which did not stop until I turned it off using the power button. When I powered the unit back on it did function correctly for a while. However I then began to notice the battery backup kicking in even though mains power was present. The usual transformer buzz which is present when operating on battery sounded different this time and it had a harsher almost sparking sound. Shortly after that the unit began to make a continuous tone and switched off again. Each time I reset it it would function for a shorter time. I believe due to failing capacitors (common heat/age related problem) the unit is struggling to detect the mains voltage accurately.

 

I followed the instructions in the linked article and it fixed by issue. Easy task for anyone with a soldering iron or a TV repair shop etc.

 

I disconnected power, removed the battery and opened up the case. For safety make sure to discharge (short out) any capacitors before you start working on the unit. Because I did not have the means to test any of the capacitors on the main circuit board I replaced all of the small 4.7uf and 22uf capacitors with new ones of the same value (105C, I used 50v but 25v also ok). This completely solved my issue and returned the unit to working condition. The transformer buzz is now quiet as it usually is when operating on battery. Happy with that and my 9 year old unit continues on for a total cost of under £4!

Attachments
  • Tags:
  • english
Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc