New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
APC Smart UPS Model: SMT1000IC - Wrong Battery Installation Date
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-07-0702:49 AM
APC Smart UPS Model: SMT1000IC - Wrong Battery Installation Date
Hi,
I recently purchased and installed a SMT1000IC UPS and when selecting the battery installation date accidentally selected the wrong date. Is there a way to reset it. I have tried to disconnect the power, and the battery at the back holding the power button for 30 seconds and turning it back on and then running the set up wizard again but the wizard does not give me the option to change the date again?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-07-0709:45 AM. Last Modified: 2026-07-0709:45 AM
There are three possible options depending upon your current environment and setup.
LCD Menu: Disconnect the Anderson connector from the RBC. Wait for the system to declare a battery fault and wait another ten seconds. Then, reconnect the Anderson connector and the system will prompt you to confirm this is a new RBC. Toggle from No to Yes than enter the correct month and year.
NMC: If the unit has an embedded or add on NMC via the Smart Slot. You can login to the NMC and navigate to Configuration -> UPS -> Last Battery Replacement -> Enter Month / Year.
Power Chute: If the APC Power Chute Software (PCSS, PCBE, PCPE) is installed simply navigate to the UPS tab and enter the month and year.
Questions Ask - If not and this answered your query please do mark this reply as a solution to help the next person asking the same. 👍