Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC NS1080 (BN1080G) does not work after power outage

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: APC NS1080 (BN1080G) does not work after power outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Wilferik
Wilferik
Explorer

Posted: ‎2024-02-27 12:40 PM

0 Likes
5
9558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-27 12:40 PM

APC NS1080 (BN1080G) does not work after power outage

A few days ago we had a 9 hours power outage and, after power was restored my APC NS1080 (BN1080G) refused to work anymore.

Battery was replaced 3 months ago, so it is new... but the device barely responds to a power button press with a quick flash of the LCD backlight and nothing else. The breaker switch on the back doesn't seem to do anything.

Already tried to unplug it from the wall, right now it is with no devices connected to it, and when reconnected to power it simply does exactly the same: A brief flash of the LCD backlight and nothing else.

Any ideas, besides looking for a replacement?

Thanks!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • bn1080g
  • english
  • ns1080
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2024-03-01 05:45 AM . Last Modified: ‎2024-03-01 05:48 AM

In response to Wilferik
0 Likes
1
9518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-01 05:45 AM . Last Modified: ‎2024-03-01 05:48 AM

The voltage you measured indicates the battery is fine / full. 👍 If the unit is still under warranty you should contact APC Technical Support to help troubleshoot the problem or if required initiate a RMA.

 

If the unit is out of warranty you can try a couple of things to see if it makes a difference. 

Brain Dead: Unplug the unit from AC Mains. Disconnect the internal battery. Press and hold the power button until you hear a click / beep. This procedure resets the unit and attempts to clear any possible errors in the system. You may not hear or see a change from the unit as the brain dead procedure is not always integrated into a specific product line. Once this procedure is done reconnect the battery and apply AC Mains. Do not connect any loads to the unit at this time. 

 

What do you observe?

 

Power On: Not all of the APC UPS models turn back on after a full depletion of the battery cells once utility power is restored. The user needs to press the power button for the unit to turn on & operate again. 🤦‍♂️🙁


NOTE: It’s important to understand there are different kinds of operational behaviours as it relates to how a unit will operate or behave under different environmental scenarios. 

Cold Start: Each manufacturer defines this differently. As such my explanation will differ from vendor to vendor. If a unit indicates a cold start feature it means it can turn on from battery only while AC Mains is not present. This obviously assumes the battery is at the operational voltage level to do so. 

 

Hot Swap: If a unit offers this ability it normally indicates the hardware can be started (turned on) without any batteries present. 

Lower end models that do not have (hot swap) abilities will NOT turn back on if a battery is missing, low battery voltage, even when AC Mains has been restored / present. 🤢

 

Charging: Some units only charge while it’s turned on. Other units charge immediately if AC Mains is present. You won’t know until you validate the unit’s behaviour. 

 


Pre-purchase: As stated up above it’s imperative to know and understand how a UPS will operate in any given state! ☝️ A simple test such as disconnecting the battery and applying AC Mains then pressing the power button. If the unit does not turn on it’s not hot swappable. 

 

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Teken
Teken
Champion

Posted: ‎2024-02-28 02:52 AM

0 Likes
3
9556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-28 02:52 AM

Assuming this is a high quality CSB (high discharge) battery inside. Measure the resting voltage of the battery with a multi meter.

 

What is the value? 🤔


Im going to assume you will see below 10 VDC. If so you can try to recharge the battery using an external 12 volt charger. Once the battery is fully charged insert the same back into the UPS.

 

The UPS should operate normally from there. 👍

 

NOTE: The behaviour you describe is because the battery voltage is too low. As such the UPS will not turn on and operate as expected. A standard APC battery can sustain (approximately) 260 full cycles before its service life is affected. The average service life is 3-5 years which depends upon usage and temperature. Repeated depletion (fully drained) cells will shorten the service life dramatically! 

Let me know how this turns out. 👍

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Wilferik
Wilferik
Explorer

Posted: ‎2024-02-28 01:35 PM

In response to Teken
0 Likes
2
9519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-28 01:35 PM

Thanks so much for the suggestion. This UPS takes a double battery (7Ah, 24V). After measuring voltage with a multimeter, it shows 27VDC.

I don't have a 12V charger available, plus the connector is recessed, very hard to reach.

Shouldn't the UPS charge the battery if it has low charge? Sounds illogical that if this happens the battery had to be taken out and charged externally.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2024-03-01 05:45 AM . Last Modified: ‎2024-03-01 05:48 AM

In response to Wilferik
0 Likes
1
9518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-01 05:45 AM . Last Modified: ‎2024-03-01 05:48 AM

The voltage you measured indicates the battery is fine / full. 👍 If the unit is still under warranty you should contact APC Technical Support to help troubleshoot the problem or if required initiate a RMA.

 

If the unit is out of warranty you can try a couple of things to see if it makes a difference. 

Brain Dead: Unplug the unit from AC Mains. Disconnect the internal battery. Press and hold the power button until you hear a click / beep. This procedure resets the unit and attempts to clear any possible errors in the system. You may not hear or see a change from the unit as the brain dead procedure is not always integrated into a specific product line. Once this procedure is done reconnect the battery and apply AC Mains. Do not connect any loads to the unit at this time. 

 

What do you observe?

 

Power On: Not all of the APC UPS models turn back on after a full depletion of the battery cells once utility power is restored. The user needs to press the power button for the unit to turn on & operate again. 🤦‍♂️🙁


NOTE: It’s important to understand there are different kinds of operational behaviours as it relates to how a unit will operate or behave under different environmental scenarios. 

Cold Start: Each manufacturer defines this differently. As such my explanation will differ from vendor to vendor. If a unit indicates a cold start feature it means it can turn on from battery only while AC Mains is not present. This obviously assumes the battery is at the operational voltage level to do so. 

 

Hot Swap: If a unit offers this ability it normally indicates the hardware can be started (turned on) without any batteries present. 

Lower end models that do not have (hot swap) abilities will NOT turn back on if a battery is missing, low battery voltage, even when AC Mains has been restored / present. 🤢

 

Charging: Some units only charge while it’s turned on. Other units charge immediately if AC Mains is present. You won’t know until you validate the unit’s behaviour. 

 


Pre-purchase: As stated up above it’s imperative to know and understand how a UPS will operate in any given state! ☝️ A simple test such as disconnecting the battery and applying AC Mains then pressing the power button. If the unit does not turn on it’s not hot swappable. 

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Wilferik
Wilferik
Explorer

Posted: ‎2024-03-03 06:16 PM

In response to Teken
0 Likes
0
9495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-03 06:16 PM

After applying the brain dead procedure the UPS came back to life. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

ept7
ept7
Explorer

Posted: ‎2025-03-03 12:09 AM

0 Likes
0
7687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-03 12:09 AM

Put mine on an external charger and both batteries showed an error on charging. Volt meter showed 27 Volts for the pair and 13 volts+ for each.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore