Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC BX1100C-IN power on led does not turn on but makes fan noise

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC BX1100C-IN power on led does not turn on but makes fan noise
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
amithm3
amithm3
Explorer

Posted: ‎2026-09-21 11:12 PM

0 Likes
6
376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-21 11:12 PM

APC BX1100C-IN power on led does not turn on but makes fan noise

my 1mo old APC BX1100C-IN was working flawlessly until today, it does not give power at all now, the charge light indicator works when I unplug and plug back in, fan makes noise, but the power on indicator is dead, the led does not illuminate at all.

I have tried everything, resetting pluging it off ac and it auto shutsdown, but when I plug ac again same issue, no power output and no led indicator. I have pressed the circuit breaker too and nothing happens.

long pressing the power button makes a long beep sound for 7sec and nothing else happens.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
amithm3
amithm3
Explorer

Posted: ‎2026-09-22 02:22 AM

0 Likes
0
358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-22 02:22 AM

okay seems like, it started working normally now, there was a brownout (low voltage from the grid/mains). now mains is stable and the UPS is working again.
its strange why it didnt work under low voltage? shouldnt it shift to battery mode and regulate the voltage?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-09-22 04:51 AM

0 Likes
4
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-22 04:51 AM

You may consider completing a brain dead reset following this resource link:

 

https://www.se.com/hk/en/faqs/FA158947/

 

If the problem is (NOT) solved by a brain dead reset I suggest you contact APC Technical Support in India. Have ready the serial number purchase receipt and brief description of the problem.

 

Let me know how everything turns out and what they do to resolve the issue besides a RMA.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

amithm3
amithm3
Explorer

Posted: ‎2026-09-22 08:34 AM

In response to Teken
0 Likes
3
358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-22 08:34 AM

yup I had tried the brain dead rest, still had'nt worked, but its working now. seems like twas a low voltage issue from the grid, there was a brownout and thats when this problem was persistent, now its back to normal and works correctly.

what boggles me is that the UPS did not work as intended, isnt it supposed to regulate the low voltage and work properly and not give me a scare like this

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-09-23 05:28 AM

In response to amithm3
0 Likes
2
347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-23 05:28 AM

I suggest you contact APC Technical Support to validate the system is working as designed.

 

Based on your feedback it obviously isn’t working properly. You can perform a simple test now and report back the results.

 

Remove AC Mains from the wall outlet. The system should immediately switch to battery only mode and the unit should beep and display the loss of AC Mains on the front LED.

 

Does that happen? If it does how long does the unit operate for? Keeping in mind if the system is fully loaded the operation runtime won’t be very long.

 

What is the total connected load on the system? 

NOTE: The sales link for your specific model UPS indicates it supports APC Power Chute Software (PCSS). If it does connect the system to a computer running the software and report back what the logs show when you complete the simulated grid down / power loss event test.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

amithm3
amithm3
Explorer

Posted: ‎2026-09-23 05:54 AM

In response to Teken
0 Likes
1
326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-23 05:54 AM

it works normally now, when I disconnected the plug off mains it switched to battery correctly and all the connected devices did not experience any fluctuations.

its operating correctly, I tested for about 10min and the power from the ups is still working and beeping, plugged it back in after 10min.

load is a 2k monitor, a 100W charger connected to a Mac, and a PS5, not sure how much load it takes at a given moment.

I will look into the PCSS thing you mentioned and get back, although its working normally now, the brownout caused something unexpected ig, is it possible that if the mains is fully down it works correctly, but if mains is on, but its running on low voltage / single phase, it does something weird and thinks the mains is working and does not require the use of the battery ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-09-24 04:09 AM

In response to amithm3
0 Likes
0
318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-24 04:09 AM

The APC product page indicates your specific unit incorporates the AVR circuit.


As such if the user defined setting is within that limit it should (buck / boost) the input voltage coming from the wall outlet.

 

Typically you can read the user manual to adjust the AVR circuit or use the APC Power Chute (PCSS) Software to do the same (IF) the USB port is available and present on the rear of the unit.

 

For whatever reason your specific unit doesn’t show any USB port yet the main page indicates PCSS is available for use?!?! 🤦‍♂️

 

The user manual also doesn’t indicate you have the ability to define the power quality, sensitivity, or AVR circuit.

 

https://download.se.com/files?p_enDocType=User+guide&p_File_Name=SPD_JGNY-A297BQ_EN.pdf&p_Doc_Ref=SP...

 

I have to gather this series of APC Back-UPS are literally the bottom of the barrel hardware SE / APC makes. 🤢

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore