New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
new network card
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-2802:00 AM
new network card
hi,
i have SUA3000RMI2U/JS0448002222 and new network card AP9640, Can I use this card with this power supply? And if so, do I need to turn the power supply off, or can it be done while it's running?
The link addresses the bulk of the information as it relates to hardware compatibility. Keeping in mind the proper firmware must be in place for AP9640 NMC.
Also depending upon what specific UPS SKU some NMC’s won’t physically fit inside because of the two side location notches on the rear housing. If this problem exists you can simply use a file to make the NMC slit wider (taller) to allow the card to slide in correctly.
The NMC is hot swappable as such you don't need to power down the UPS.