Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

configuring PCNS with two differents UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: configuring PCNS with two differents UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:34 AM

0 Likes
2
288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:34 AM

configuring PCNS with two differents UPS

This question was originally posted by moussa on APC forums on 3/31/2014


Hello,

i want your help on this point.

We have two APC UPS:

- One MGE Galaxy 5000 with a 66074 network management card

-One SURT6000XLI with a AP9631 network management card.

These UPS provide power supply for all of our servers. each server has two power supplies, each one connected to an UPS.

We would like to configure PCNS to shutdown the servers when these two UPS lost both their power source. Reading the APC documentation i've seen that this is call redundant UPS configuration. But also in these documents it's said that the two UPS must be the same model and type. Is this the case ?

Should i really have two UPS with the same model to achieve this? If yes, is there any solution i could follow to do this configuration. If no, What is the best way to achieve my goal ?

thank in advance.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:34 AM

0 Likes
0
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:34 AM

This reply was originally posted by Bill on APC forums on 4/1/2014


Hi,

Unfortunately the Galaxy 5000 is not supported in a redundant configuration. The 5000 is designed for parallel redundant or parallel UPS configuration with the AP9635CH card installed. Application Note 169 discuss this.

Application Note 98 discusses SURT6000 with redundant UPS configuration. The SURT models UPS can be configured redundantly but the other UPSes need to be SURT models as well.

See Answer In Context

Reply
Share
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:34 AM

0 Likes
0
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:34 AM

This reply was originally posted by Angela on APC forums on 4/1/2014


The MGE 66074 does not work with PowerChute Network Shutdown, only the MGE Network Shutdown Module software I believe. So, I don't think that you'll be able to get this to work unless you had two APC Network Management Cards, one in each UPS. But, Bill P., I know we had a question recently on using a Symmetra LX and PX together and there was no problem with that, but was it only because they are both "Symmetras" of some type? If mcoly somehow got an APC Network Management Card in his Galaxy UPS, would that be allowed like the Symmetra LX/PX is? Or is it too different?

Depending on your model of Galaxy 5000/5500 (and what Bill P can clarify), some of them can be converted to an APC AP9635CH Network Management Card but you'd have to have your local technical support verify the exact UPS model and serial number to see if it can be converted to use an APC Network Management Card instead of the MGE 66074.

While we recommend the same type of UPS in general, you might run into configuration problems with different types of UPSs, and the events they support within PowerChute Network Shutdown if you got this working if it works at all. And, we have not tested this type of thing so you may have to spend a little time verifying there are no unforeseen circumstances if we got this far.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:34 AM

0 Likes
0
286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:34 AM

This reply was originally posted by Bill on APC forums on 4/1/2014


Hi,

Unfortunately the Galaxy 5000 is not supported in a redundant configuration. The 5000 is designed for parallel redundant or parallel UPS configuration with the AP9635CH card installed. Application Note 169 discuss this.

Application Note 98 discusses SURT6000 with redundant UPS configuration. The SURT models UPS can be configured redundantly but the other UPSes need to be SURT models as well.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc