APC UPS Data Center & Enterprise Solutions Forum
Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.
Posted: 2021-06-30 11:24 PM
This question was originally posted by Ogawa on APC forums on 4/5/2011
Hello
I have a Smart-UPS with a Windows 7 PC, using PowerChute Agent and managing it by http://localhost:3052/ .
I have been using PowerChute 9.0, uninstalled to install the new 9.0.1.606. After that I realized that Windows Power Options disappeared. I guess that it's to prevent confusions between witch program decide when to Shutdown the machine? but in my case I was using Windows' options for the settings. This is because on a blackout I set the PC to reduce CPU usage, turn off the HDD and turn off the Monitor in few minutes so the UPS can hold more time till the electricity comes back.
There is an option for disabling Shutdown on Low Battery in PowerChute managing page, but can't enable the Windows Power Options to lower the energy use and to Hibernate on Low Battery.
Hope there is a way to re-enable it, or at least for the future versions of PowerChute to have this option.
Thanks.
Posted: 2021-06-30 11:24 PM
This was originally posted on APC forums on 4/13/2011
i took the time to register on this forum just to say THANK YOU!
can't believe such a simple fix could be so obscure and hard to find!
THANKS again!
Message was edited by: Manp
Posted: 2021-06-30 11:24 PM
This reply was originally posted by Angela on APC forums on 4/5/2011
[this should help|http://nam-en.apc.com/app/answers/detail/a_id/11271]
Posted: 2021-06-30 11:24 PM
This was originally posted on APC forums on 4/13/2011
i took the time to register on this forum just to say THANK YOU!
can't believe such a simple fix could be so obscure and hard to find!
THANKS again!
Message was edited by: Manp
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.