Will SRT192RMBP2 work as a battery pack for SURT6000XLT-1TF3

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Will SRT192RMBP2 work as a battery pack for SURT6000XLT-1TF3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Jarrett
Jarrett
Cadet

Posted: ‎2023-11-27 01:27 PM

0 Likes
2
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-27 01:27 PM

Will SRT192RMBP2 work as a battery pack for SURT6000XLT-1TF3

They are both 192v so I would think so, but would like to confirm with the experts. I have an opportunity to acquire a cheap SRT192RMBP2 after recently acquiring a SURT6000XLT-1TF3 but want to ensure that it will function ok as a battery pack for extended runtime. Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Spock Teken
Spock

Posted: ‎2024-02-09 09:22 AM

1 Like
1
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-09 09:22 AM

For the benefit of others who may be considering doing something like this. Here are some things to keep in mind if caution is being cast to the wind. As this is obviously not endorsed, recommended, or supported by APC.

 

1. Connector: The plug that inserts into the main system will be different and thus you would need to find the same. The factory SRT cable is encased with several ferrites to reduce EMI / RFI and to meet emissions so do not remove them. It will probably be easier to make an adaptor cord set to mesh the two together so it leaves the SRT intacted.

 

2. ID: Newer APC models use a combination of resistance and IC's to tell the main system an extended battery pack is present and the quantity. You will need to determine if this is a simple circuit using resistors vs a more complex one which incorporates both. You can obviously open the SRT to review the PCB inside to see what is being used but you would need to know what (is / was) being used in the SURT model.

 

Older APC UPS simply had you tell the main system how many extended battery packs were present either through the main LCD Menu or via Power Chute software / NMC.

 

Good luck and let us know how that turned out . . .

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 2
Teken
Spock Teken
Spock

Posted: ‎2024-02-09 09:22 AM

1 Like
1
487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-09 09:22 AM

For the benefit of others who may be considering doing something like this. Here are some things to keep in mind if caution is being cast to the wind. As this is obviously not endorsed, recommended, or supported by APC.

 

1. Connector: The plug that inserts into the main system will be different and thus you would need to find the same. The factory SRT cable is encased with several ferrites to reduce EMI / RFI and to meet emissions so do not remove them. It will probably be easier to make an adaptor cord set to mesh the two together so it leaves the SRT intacted.

 

2. ID: Newer APC models use a combination of resistance and IC's to tell the main system an extended battery pack is present and the quantity. You will need to determine if this is a simple circuit using resistors vs a more complex one which incorporates both. You can obviously open the SRT to review the PCB inside to see what is being used but you would need to know what (is / was) being used in the SURT model.

 

Older APC UPS simply had you tell the main system how many extended battery packs were present either through the main LCD Menu or via Power Chute software / NMC.

 

Good luck and let us know how that turned out . . .

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Jarrett
Jarrett
Cadet

Posted: ‎2024-02-26 08:51 AM

In response to Teken
0 Likes
0
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-26 08:51 AM

Thanks for the information. I never tried it because I was waiting for a response before proceeding and will not be attempting this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of