Warmstart notification - SMART-UPS 6000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
connie.cook_apc
Ensign
Ensign
0 Likes
2
268

Warmstart notification - SMART-UPS 6000 XL

This was originally posted on APC forums on 11/19/2012


This morning, I received a notification that my UPS performed a warmstart. This is the first time this has happened and I have attempted to review the knowledgebase and other articles, but each time to click on the link to the support article, I am asked for the model of my UPS and then it just goes to the main support page. I have not been able to really read anything useful, so I must post in here to see if someone can assist me.

Here is some information regarding my unit:

11/19/2012 06:31:14 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Int Sensor at Int Sensor Loc) communication.
11/19/2012 06:30:23 UPS: Restored the local network management interface-to-UPS communication.
11/19/2012 06:25:33 UPS: Passed a self-test.
11/19/2012 06:25:17 UPS: Started a self-test.

Hardware Factory
Model Number: AP9619
Serial Number: NA0835009156
Hardware Revision: A10
Manufacture Date: 08/29/2008
MAC Address: 00 C0 B7 D2 91 D9
Management Uptime: 0 Days 3 Hours 52 Minutes
Application Module
Name: sumx
Version: v3.7.2
Date: 02/02/2010
Time: 19:08:16
APC OS (AOS)
Name: aos
Version: v3.7.3
Date: 02/02/2010
Time: 17:05:14

I've also attached my config.ini, event.txt and data.txt.

I would just like to be able to figure out what could have caused the warmstart and if there is a problem that I need to fix.

Many thanks!
Connie


Accepted Solutions
connie.cook_apc
Ensign
Ensign
0 Likes
0
268

Re: Warmstart notification - SMART-UPS 6000 XL

This was originally posted on APC forums on 11/19/2012


Thank you very much. I appreciate the information.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
267

Re: Warmstart notification - SMART-UPS 6000 XL

This reply was originally posted by Angela on APC forums on 11/19/2012


is this the site you were researching? http://www.apc.com/site/support/index.cfm/faq/

if not, please see if you can search for FA156063 there to review the knowledge base article on this topic.

looking at your logs, i would not be too concerned. it does not mean the UPS rebooted, only the network management card interface. the NMC generally does this as a failsafe to clear up any issues it might detect (i.e. if it cannot ping its default gateway). as long as it is not happening constantly/repeatedly, i would not worry.

connie.cook_apc
Ensign
Ensign
0 Likes
0
269

Re: Warmstart notification - SMART-UPS 6000 XL

This was originally posted on APC forums on 11/19/2012


Thank you very much. I appreciate the information.