Upgrade APC Smart-UPS 1500 (SUA1500i) to LiFePo4
  • Re: Upgrade APC Smart-UPS 1500 (SUA1500i) to LiFePo4
BillP Leader
5059
196
Teken
Teken
162
Free
English
4.0
Register Browse SE University
Hyper.nl
Hyper.nl
Explorer
Posted: ‎2023-03-10 08:42 PM . Last Modified: ‎2023-03-10 08:47 PM
11
55609
Hm, I used to have an account at the APC.com forums, but it seems to have been deleted. (Last login around 2018)
I started a small project for myself to upgrade my older APC Smart-UPS 1500 (SUA1500i) from AGM SLA batteries to LiFePO4 batteries with advanced BMS. Normally UPS units that are designed to work with SLA batteries are not compatible with LiFePO4 batteries, some battery manufacturers have designed an advanced BMS (Battery management system) that allow LiFePO4 batteries to be used in any application where SLA batteries are normally used.
I used 12v 30Ah PowerBrick+ batteries from PowerTech systems. These are fairly expensive but they should last a lot longer than traditional SLA batteries. These batteries can have 3000 cycles at 100% DoD or 4500 cycles at 80% DoD.
This guide should work for any Smart-UPS that uses the same batteries and same connector (APC RBC7)
https://youtu.be/tSfOPcbxAqk
This video is not sponsored. I bought the batteries myself.
Using LiFePO4 batteries in APC units made for SLA batteries is NOT supported by APC.
See video description for important information.
Replies 11
Javik_apc
Javik_apc
Contributor
Posted: ‎2023-05-11 01:38 PM
I am very interested in these LiFePO4 substitution projects, because lead-acid is just a horrible technology, and APC's battery monitoring and failure detection has been technically deficient forever. A LiFePO4 BMS substitution may not be built to APC's intended usage, but their "intended usage" is terrible also.
At this very moment I have an APC 1500va LED with a dead APC RBC7 battery pack in a small server room, but which the UPS believes there are no problems with the RBC7. If I run a manual self-test it drops the load and the Dell PowerEdge server R630 suddenly turns off!
Nice work there APC, I thought you fixed this faulty technical implementation and moved over to using resistive simulation loads for self testing, when your products changed from beige to black.
So anyway, a specific problem that you may experience with your LiFePO4 is that the onboard BMS needs to pretend it is a lead-acid battery, and slope the output voltage up and down as the LiFePO4 discharges.
You do NOT want a BMS that outputs a steady "full-charge" voltage of 13.6v until the lithium battery is discharged, at which point the BMS suddenly turns off.
This defeats the UPS from being able to determine the state of discharge by monitoring the battery voltage as it discharges. The UPS will have no way of knowing when to enter the "low-battery" phase and send the alert signal that the server should start the automatic shutdown or suspend procedure, to prepare for loss of power.
Ideally the BMS output voltage should slope down to approximate the declining state of charge of a lead-acid battery as the LiFePO4 discharges.
Also it may potentially be better to use a 24 volt LiFePO4 with the same approximate size as the two 18ah lead-acid batteries next to each other. This allows for bigger cooling heatsinks in the combined BMS, fewer BMS components to fail, and also larger lithium cells in the unpartitioned bottom casing.
Hyper.nl
Hyper.nl
Explorer
Posted: ‎2023-05-11 02:06 PM
1
55455
The usage of a single 24V LiFePO4 battery is actually quite a nice idea. It may help to prevent any balance issues, if any. I just took 2x 12V replacements to stay the nearest to what the APC expects.
PowerTech Systems also has a 24v variant. The connectors will be at a different place and you need to check if the physical dimensions are right for this unit.
https://www.powertechsystems.eu/wp-content/uploads/specs/PowerBrick_PRO+_24V_32Ah_Lithium-Ion_batter...
Javik_apc
Javik_apc
Contributor
Posted: ‎2023-05-11 03:05 PM
In response to Hyper.nl
Also there is another problem with these LiFePO4 substitutions. You need to carefully examine the specifications for the substitute battery to make sure the onboard BMS can actually output the full capacity of the original lead-acid battery pack, for the maximum load watts for the UPS.
In the UPS I am discussing here: APC SMT1500 - Maximum load 1000 watts, 1500 VA
Lead acid battery, general characteristics:
  • Full charge = 13.6v * 2 = 27.2 volts
  • Full discharge = 10.5v * 2 = 21.0 volts
As any kind of battery discharges, gradually the amperage increases:
  • 1000 watts / 27.2 volts = 36.7 amps
  • 1000 watts / 21.0 volts = 47.6 amps
The PowerBrick 12v / 30ah Standard will not work for this, but the PowerBrick Pro+ can do it... nearly.
(Whether the Pro+ actually drops to 21.0v at end of lithium discharge, I don't know.)
https://www.mylithiumbattery.com/shop/12v-lithium-ion-battery-packs/lithium-battery-12v/lithium-ion-...
Standard:
  • Maximum continuous current: 30 amps
  • 30 second peak current: 45 amps
Pro+:
  • Maximum continuous current: 45 amps
  • 30 second peak current: 70 amps
Meanwhile this lower-quality 12v LiFePO4 of a similar physical size from ExpertPower is pretty much useless:
https://www.expertpower.us/products/ep1220-20ah
ExpertPower EP1220
  • Continuous current: 20 amps
  • Permanent discharge: 45 amps for 2 seconds
You would have to use two of the much larger ExpertPower battery that won't physically fit in the APC 1500VA battery compartment.
https://www.expertpower.us/products/ep1250-50ah
ExpertPower EP1250
  • Continuous current: 50 amps
  • Permanent discharge: 100 amps for 10 seconds
For people that are not buying quality LiFEPO4 with a built-in drop-in 12v/24v BMS, there is the potential to be severely disappointed if their cheap PongHuan Fzdagbu Amazon battery for US $50 fails at the worst possible moment because it can't handle more that 20% the UPS maximum rated load capacity... lol
alvesjc
alvesjc
Explorer
Posted: ‎2023-12-02 03:24 PM
52278
I just converted my very old but great SmartUPS 1400RMXLNET to LiFePo4.
I used the Daly BMS plus active balancer pack, and the battery pack is 16S3P of 32650 6AH cells.
It's working fine but had some fights to start the UPS, it took a while to let me start the UPS.
What I'm noticing here, is that the battery pack is not being fully charged, the cels are a 3.40V aprox and aren't charged anymore.
From what I've understood, the UPS only trickle charges to 13.6V per 12V battery what matches the 54.4V I currently have in the pack.
Is there a way to change this voltage to a bit higher value to have a better usage of the cells capacity?
The BMS cuts at 3.65V per cell, If I could make the UPS charge up to 3.6V would be great, and still before the BMS cuts the pack.
DZelmer
DZelmer
Explorer
Posted: ‎2024-08-12 08:11 PM
In response to alvesjc
There might be look up the smart signaling for the ups you might beable to change the float voltage my logging in with a terminal. Need the smart signaling cable. 2nd option is do a little creative soldering and adding a 20 turn potentiometer resister to the float voltage circuit. I did that to several apc ups's incliluding some matrix units and think the otheres were smart ups 1000 lcd and some pre lcd ones. They seem to run good other than the runtime and battery% are way off. But they run good otherwise.
alvesjc
alvesjc
Explorer
Posted: ‎2024-08-14 01:26 AM
Hi @DZelmer
I got a schematic from it, can you tell me what resistor you're talking about?
For the cable, is that a standard null modem cable connected in the rear port ?
Thanks for the inputs.
alvesjc
alvesjc
Explorer
Posted: ‎2024-08-14 04:40 AM
40454
Hi @DZelmer
are you refering to voltage devider formed by R216 and R184 in the schematic ?
Picture attached.
DZelmer
DZelmer
Explorer
Posted: ‎2024-12-08 10:25 AM
I do beleve so.
I didn't even know you had another question been a long time since i logged in her.
DZelmer
DZelmer
Explorer
Posted: ‎2024-12-08 10:38 AM
So far i have been using some dakota lithium batteries on my old matrix float voltage is at 13.8 per battery 48 volt system so x4 for system voltage i think thats about 80% soc for these batteries my main problem was each battery getting off balance. I actually have 3 sets of batteries onnthe system and with out a active balancer the batteries are mismatched capacity new batteries also that they get out of balance and 1 of the bms's for each set of batteries will go in to over voltage protection and make the imbalance even worse so when the ups dose a test or tries to support the load when the power drops it just shuts off because the bms can't turn its self back on fast enough when the voltage drops. I put a active balancer on each set of batteries and i have had no problems for over a year with this setup including a power outage that i wasn't around for the beginning of which ran the batteries down until the ups shut down. Not sure if it did it gracefully or not but it didn't trip any of the bms's for low voltage. When instarted the generator it started charging. 2 of my small ups's on the other hand tripped 1 of the bms for low voltage and i had to put a lithium charger on the battery to wake it up and turn the ups back on to charge it pretty sure a active balancer will fix that problem also.
ChongLiu
ChongLiu
Explorer
Posted: ‎2025-02-06 12:05 AM
Lead acid battery general characteristics:
24V configuration:
48v configuration:
Full charge = 13.6v * 4 = 54.5 volts
Full discharge = 10.5v * 4 = 42.0 volts
LifePO4 battery general characteristics:
48v 16S configuration:
Full charge = 58.4 volts
Full discharge = 40 volts
48v 15S configuration:
UPS Full charge = 54.4 volts
Full discharge = 37.5 volts
When UPS Discharge set point = 42.0 volts, the LifePO4 battery still has about 5% of capacity.
So, 15S LifePO4 configurations is almost perfect match for 48v Lead acid batteries configuration.
Lefteris
Lefteris
Explorer
Posted: ‎2026-06-02 09:26 AM
1 LiFePO4 12V 18Ah costs like 6 lead acid ones. With a life span of 5-15yrs max, even the max is still almost half the price for the lead acid ones over the same period of time. Not only that, but they need to be checked so often for correct charge otherwise might just boom! That is a really nono for me.