Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Unable to update firmware v15.0 from https://smartconnect.apc.com - Check UPS State

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Unable to update firmware v15.0 from https://smartconnect.apc.com - Check UPS State
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
tracyCheAsta
Crewman tracyCheAsta
Crewman

Posted: ‎2022-04-21 02:32 AM . Last Modified: ‎2022-04-21 06:53 AM

2 Likes
17
3631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-21 02:32 AM . Last Modified: ‎2022-04-21 06:53 AM

Unable to update firmware v15.0 from https://smartconnect.apc.com - Check UPS State

UPS NAME

SCL500RM1UC

MODEL NAME

Smart-UPS 500

 

The current UPS state is not compatible with running a firmware upgrade, please check the UPS Status page for more information. For example, check your UPS is not On Battery, and for issues such as Overload or Temperature Threshold Exceeded. See the Help Center for troubleshooting advice or contact Customer Support for further assistance.

-------------------------------------

 

I received a firmware update available notification on https://smartconnect.apc.com. I tried to run firmware update from the portal but received the above error message every time. I tried to shut down the UPS and performed diagnostics several times. Diagnostic test passed.

 

Battery temperature is 77°F. I couldn't understand what was preventing the firmware upgrade process.

 

Any further help would be appreciated.

 

Thank you.

 

EDIT 1:

I just read this doc https://www.smartconnect-support.apc.com/help/en/index.html#page/EcoStruxure%20Ready%20Smart-UPS%20H... and it says that "Make sure that the UPS is installed in a cool, dry location. Check that the ambient temperature of the UPS installation site does not exceed 24º Celsius/ 75º Fahrenheit."

 

Does the temp needs to be at 75F in order to run the firmware upgrade?

 

EDIT 2:

I adjusted air conditioner and retried the upgrade process from the portal while the temp of the UPS is at 73F. It failed again stating that UPS state is not allowing the update to start.

 

Any thoughts?

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-05-03 01:05 PM

In response to marmstrong
0 Likes
7
3053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-05-03 01:05 PM

Hi,

 

To correct this issue, you must power down the connected load, power off the UPS, then log into SmartConnect.apc.com and run the firmware upgrade. The UPS must remain plugged into AC and connected to the cloud for the upgrade to run. Once the upgrade has been completed, you can power on the UPS and power up the load.

 

NOTE: This issue will be addressed in a future UPS firmware release.

See Answer In Context

  • Tags:
  • english
Reply
Replies 17
Sados
Sados
Cadet

Posted: ‎2022-04-21 08:19 AM

0 Likes
13
3596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-21 08:19 AM

We're running into the same problem on a SCL500RM1UC. Didn't have any issues upgrading the firmware a few weeks ago. Got the alert today new firmware was available and we got the exact same error your are. I feel like it's an issue with the new firmware itself or APC put in some other check that we're not meeting causing it to not install. If it is due to temperature, not much we can do about temperature when its in a server rack in a climate controlled room already. We're showing 86F but there's no changing that. It's better than the God awful 100+ range years ago. If there's no way around the temp requirement we would have to power down all servers and take the UPS out of the server room and cool it down somewhere else just to upgrade it. That is definitely not happening. 

  • Tags:
  • english
Reply
tracyCheAsta
Crewman tracyCheAsta
Crewman

Posted: ‎2022-04-21 11:23 AM

In response to Sados
0 Likes
12
3565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-21 11:23 AM

@Sados Thank you for your reply. Sorry to hear that you too are facing the same problem. I read the CVE https://www.cisecurity.org/advisory/multiple-vulnerabilities-in-schneider-electric-apc-smart-ups-cou... and unplugged Ethernet cable from the UPS as a safer measure. Let's see if someone from APC support can weigh in here.

  • Tags:
  • english
Reply
kja
kja
Cadet

Posted: ‎2022-04-22 06:50 AM

In response to tracyCheAsta
0 Likes
11
3507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-22 06:50 AM

Same unknown issue causing failure to upgrade on two SCL500RM1UC in different locations, both with nominal loads and temperatures (76F and 67F). Likely a firmware patch issue with this SCL500RM1UC model as I successfully updated a SMT3000RM2UC a few weeks ago.

  • Tags:
  • english
Reply
JTBearcat
Crewman JTBearcat
Crewman

Posted: ‎2022-04-22 08:40 AM

In response to kja
1 Like
1
3488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-22 08:40 AM

I have the same issue. Some help would be appreciated.

  • Tags:
  • english
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-04-22 10:12 AM

1 Like
1
3472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-22 10:12 AM

@tracyCheAsta 

 

I am looking into this and will follow-up once I have more information. 

  • Tags:
  • english
Reply
tracyCheAsta
Crewman tracyCheAsta
Crewman

Posted: ‎2022-04-22 10:16 AM

In response to JTBearcat
0 Likes
0
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-22 10:16 AM

Sounds good. Thank you!

  • Tags:
  • english
Reply
LReimer
LReimer
Cadet

Posted: ‎2022-04-22 10:17 AM

In response to BillP
1 Like
0
3465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-22 10:17 AM

I am having the same issue... waiting for a resolution.

  • Tags:
  • english
Reply
bmw528eta
bmw528eta
Cadet

Posted: ‎2022-04-25 05:58 AM

0 Likes
0
3361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-04-25 05:58 AM

Same here with a SCL500RM1UC.

I bet something in their firmware rollout is broken....good thing it still works

  • Tags:
  • english
Reply
marmstrong
marmstrong
Cadet

Posted: ‎2022-05-03 08:29 AM

In response to kja
0 Likes
8
3072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-05-03 08:29 AM

Same here: worked on my SLC750RM2UC but won't work on any of my SCL500RM1U units.

  • Tags:
  • english
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-05-03 01:05 PM

In response to marmstrong
0 Likes
7
3054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-05-03 01:05 PM

Hi,

 

To correct this issue, you must power down the connected load, power off the UPS, then log into SmartConnect.apc.com and run the firmware upgrade. The UPS must remain plugged into AC and connected to the cloud for the upgrade to run. Once the upgrade has been completed, you can power on the UPS and power up the load.

 

NOTE: This issue will be addressed in a future UPS firmware release.

  • Tags:
  • english
Reply
tracyCheAsta
Crewman tracyCheAsta
Crewman

Posted: ‎2022-05-10 02:07 AM

In response to BillP
0 Likes
0
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-05-10 02:07 AM

Hi Bill,

 

Thank you so much for your prompt update.

 

I followed your advice and was able to upgrade firmware successfully for SCL UPS.

  • Tags:
  • english
Reply
ITDepartment
ITDepartment
Cadet

Posted: ‎2022-05-13 06:28 AM

In response to BillP
0 Likes
5
2795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-05-13 06:28 AM

Hello Bill,

 

Thank you for providing that solution. I am looking to clarify the comment about this issue being fixed in a future firmware release. Does that mean the following?

 

A) If we wait a bit, a different firmware update will let us perform the update through the website without having to use the power down procedure you provided. 

 

OR

 

B) The future firmware will allow us to update without powering down the load, however we have to go through the power down procedure with the current firmware to get there. So there is no way of avoiding the power down aspect here, even if we wait for the new firmware.

 

Maybe a C) that I am not aware of. 

 

The headache here a lot of these units are likely protecting Internet related gear in branch offices. Powering down the load means no Internet. We will have no choice but to have someone on site move power cables around. 

 

Thank you. 

  • Tags:
  • english
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-05-13 07:43 AM

In response to ITDepartment
1 Like
4
2791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-05-13 07:43 AM

@ITDepartment 

 

The answer is B. 

 

A future firmware will allow an update without powering down the load, however you have to go through the power down procedure with the current firmware to get there. So there is no way of avoiding the power down aspect here, even if you wait for the new firmware.

  • Tags:
  • english
Reply
JTBearcat
Crewman JTBearcat
Crewman

Posted: ‎2022-06-13 10:38 AM

In response to BillP
0 Likes
1
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-06-13 10:38 AM

I was able to update my 3U unit by unplugging all the equipment usually being protected by the UPS. But that didn’t work on the 1U unit. How do I turn off the output power on my 1U units so I can update the firmware?

  • Tags:
  • english
Reply
bmw528eta
bmw528eta
Cadet

Posted: ‎2022-06-13 10:48 AM

In response to JTBearcat
0 Likes
0
2255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-06-13 10:48 AM

Literally just hold down the power button on the front of the unit, that turns off the outlets. Yeah I had the same question and just tried that on a whim.

  • Tags:
  • english
Reply
DCS-LLC
DCS-LLC
Cadet

Posted: ‎2022-06-20 05:29 PM

In response to BillP
0 Likes
1
2105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-06-20 05:29 PM

In what version will this be corrected?  We are deploying these in remote sites, so the prospect of shutting down all hardware they are protecting just to update the firmware is a bit.. Troublesome.

I'm sitting on a SCL500RM1UC in the lab testing which is pending a V15.1 update which requires shutdown.

Current FW Version from the portal: v 02.3 (1030).

 

From the release notes:

Version: UPS 15.1 Applicable SKU: ID 1030 sku.

SCL: SCL500RM1UC, SCL500RMI1UC, SCL500RM1U
This release includes remediation for the security vulnerabilities listed as CVE-2022-22805,

CVE-2022-22806 and CVE-2202-0715 which,
if compromised, may allow potential unauthorized access and control of the device.

Change logs:

1. Function implemented to disable UPS firmware upgrades via NMC to mitigate potential risk of malicious UPS firmware being passed through this channel.

2. Enhanced UPS firmware code protection to mitigate the vulnerabilities of unauthorized extraction of confidential firmware and un-authorized network access to SmartConnect UPS.

3. Fix an issue to make the upgrade with Output On feature more stable.

Note: The previous versions may refuse the upgrade with Output On in some special situation. In such cases, please choose a suitable time when the UPS can be turned off without

affecting the use of equipment connected to the UPS. Turn off the UPS manually and then upgrade.

 

Does this mean that as long as we're on v15.1 in the future we should not have to shutdown the load to update?  Just confirming.

  • Tags:
  • english
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-06-21 06:34 AM

In response to DCS-LLC
0 Likes
0
2089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-06-21 06:34 AM

@DCS-LLC 

 

Does this mean that as long as we're on v15.1 in the future we should not have to shutdown the load to update?  Just confirming.

 

Correct. 

  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc