Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

UPS on battery power [0008] when Self-Test started

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: UPS on battery power [0008] when Self-Test started
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
OskarsAdaptive
OskarsAdaptive
Cadet

Posted: ‎2025-06-06 12:19 AM

0 Likes
4
154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-06 12:19 AM

UPS on battery power [0008] when Self-Test started

Hello, our client has 3x APC Smart-UPS Ultra 5000 SKU: SRTL5KRM2UI. Due to that these UPS devices used to have critical problems, until we updated firmware, we have to document every little problem, and this week we had our first this year.. with one of devices.

Problem - On battery power in response to an input power problem [0008].

I understand that this is pretty common error, due to that electricity tends to behave strangely, but looking at the log, this error happened at the same time Self-Test started, and I have not seen this before, so I wanted to know, if this is some kind of a bug, or this happens from time to time. Errors like these in the middle of night might cause a panic.

 

Log:

 06/03/2025 02:27:15 Device UPS is online.
 06/03/2025 02:27:15 Device No longer on battery power.
 06/03/2025 02:27:14 Device Self-Test finished.
 06/03/2025 02:26:53 Device Self-test started by the UPS.
 06/03/2025 02:26:53 Device UPS is no longer online.
 06/03/2025 02:26:53 Device On battery power in response to an input power problem [0008].

 

How should i document this problem. Thank you.

 

Regards,

Oskars

Labels
  • Labels:
  • Datacenter UPS
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Spock Teken
Spock

Posted: ‎2025-06-09 06:00 AM

0 Likes
0
136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-09 06:00 AM

You’ll need to provide the extended logs for the following: Event, Data, UPS.


Along with a screen shot of the About tab for both UPS / NMC.

 

Questions Ask . . . 👍

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

OskarsAdaptive
OskarsAdaptive
Cadet

Posted: ‎2025-06-09 11:18 PM

0 Likes
1
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-09 11:18 PM

I have added screenshots about UPS/NMC, also log.txt and power event upselog.txt from the day error occured.

 

OskarsAdaptive_0-1749535881956.png

 

OskarsAdaptive_1-1749535924753.png

 

 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-06-10 04:55 AM

In response to OskarsAdaptive
0 Likes
0
109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-10 04:55 AM

You’ll need to provide the entire logs not just for this time period: Event, Data, UPS

 

Questions Ask . . . 👍

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

OskarsAdaptive
OskarsAdaptive
Cadet

Posted: ‎2025-06-12 03:40 AM

0 Likes
0
78
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-12 03:40 AM

I have attached full logs. Event log was clear.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of