Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

UPS and Backup Generator Compatibility

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: UPS and Backup Generator Compatibility
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Moto
Crewman Moto
Crewman

Posted: ‎2025-06-02 07:34 PM

0 Likes
6
266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-02 07:34 PM

UPS and Backup Generator Compatibility

Hi All,

I am doing research about compatibility between backup generatro and UPS, for data center, and

I would like to know how sensitive backup generator frequency deviation is for data center UPS.

Below is my understanding, but I am neither generator expert nor UPS expert. So, correct me if I am wrong.

 

Say, mains fail, and backup generator start up, then suppies power to facility load.

UPS fill the gap from mains failure to generator power supply.

After that, UPS receives incoming power generated by backup generator.

When, large load is instantly applied/or rejected, backup generator frequency could be out of limit that UPS is requesting to incoming power. In that case, UPS will be on backup mode (uses its battery).

However, backup generator frequency should come back to stable shortly, thanks to governor.

I think UPS will go back to normal mode(sync with generator again) from backup mode.

So, even if such frequency deviation occurs several times, it will not affect entire operation. 

 

Any input/comment/advice will be appreciated.

 

Have a good day !!

 

Moto

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Spock Teken
Spock

Posted: ‎2025-06-05 05:00 AM

In response to Moto
0 Likes
1
198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-05 05:00 AM

You may also review this APC White Paper to understand the different types of UPS systems:

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_SADE-5TNM3Y_EN

 

You’ll probably find during your research that a Online / Double Conversion UPS is the recommended topology when speaking about mating with a generator.

 

As stated earlier only a live test and short / long term evaluation will affirm what specific model & topology will work for your specific environment and conditions.

 

Regardless of all the above an external maintenance bypass must be part of the solution to allow you and the company the ability to perform maintenance and switch over to generator power when necessary.

 

If any of the replies provided the answers you needed. Please do mark those specific replies as a solution so it may help the next person asking the same! 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Teken
Spock Teken
Spock

Posted: ‎2025-06-03 05:38 AM

0 Likes
5
250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-03 05:38 AM

All parameters relating to power quality is essential when speaking about a UPS and Generator.

 

All of the enterprise class UPS have some adjustment for frequency deviation. I suggest you contact your local MSP / APC provider to outline the requirements and hardware in place.

 

They may be able to offer you a demo unit to help validate if the UPS under review is compatible with the generator.

 

The only true test and validation is having the exact UPS System in place and see how it behaves and performs.

 

NOTE: It’s imperative to have a maintenance bypass in place. Do not rely on any internal UPS bypass if available!

 

Questions Ask . . . 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

Moto
Crewman Moto
Crewman

Posted: ‎2025-06-03 05:12 PM

In response to Teken
0 Likes
4
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-03 05:12 PM

Many thanks for your comment !

So, you suggest we should not rely on battery mode.

Any specific reason ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-06-04 04:08 AM . Last Modified: ‎2025-06-04 01:06 PM

In response to Moto
0 Likes
3
219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-04 04:08 AM . Last Modified: ‎2025-06-04 01:06 PM

I’m not sure where you got that from?!? So I’ll try to offer a little more insight and clarification.

 

Generator: In almost all cases an existing generator is in place within a building. More often than not this old and existing generator is no longer operating like new and outputs dirty power.

 

As such you’ll quickly find out upon the monthly generator test or during a grid down event that the *New UPS* does not operate and perform as expected.

 

The most common behaviours you’ll see is the unit will not switch back to online. Thus draining the internal battery cartridge which quickly degrades the battery health and service life.

 

Other scenarios are the unit will switch back and forth between online & battery. This causes the internal relays to arc and finally weld together causing a hard fault.

 

As noted here this is why an external maintenance bypass must be incorporated to allow and ensure the UPS can be bypassed for service or out of band operational behaviour.

 

You can read in this forum alone how many times a customer started a thread about the internal bypass failing or not working as expected! 🤦‍♂️

 

As such there was no (Quick Way) or method to route power to the attached loads without doing so manually which is no small feat in a data center or where there isn’t sufficient PDU outlets / cable length etc.

 

As noted also the usual steps are to define the requirements, environment, and submit a RFP. 

Typically a power quality audit / analysis is conducted and performed to determine the sites true power health. Armed with this critical information the end user will know the power is fine or not.

 

If not, than this gives the client the time to address those issues prior to the next step. Which would be to request a demo unit to help test, monitor, and validate the target (UPS) device operates as expected within the generator environment that exists.

 

Almost every APC Enterprise UPS offers the ability to define the sensitivity, upper & lower input transfer voltage, frequency deviation, and some the slew rate.

 

Other models allow the user to define the bypass threshold, and in older models Power Quality etc.

 

Regardless of all the above only a live test will allow you and the company any material facts and the data to make an informed decision prior to spending thousands of dollars on any UPS.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Moto
Crewman Moto
Crewman

Posted: ‎2025-06-04 08:45 PM

In response to Teken
0 Likes
2
201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-04 08:45 PM

Sorry, I misinterpreted internal maintenance operation. It is not battery operation.

Your further explanation is so helpful for my understanding !

I really appreciate your help.

👍

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-06-05 05:00 AM

In response to Moto
0 Likes
1
199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-05 05:00 AM

You may also review this APC White Paper to understand the different types of UPS systems:

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_SADE-5TNM3Y_EN

 

You’ll probably find during your research that a Online / Double Conversion UPS is the recommended topology when speaking about mating with a generator.

 

As stated earlier only a live test and short / long term evaluation will affirm what specific model & topology will work for your specific environment and conditions.

 

Regardless of all the above an external maintenance bypass must be part of the solution to allow you and the company the ability to perform maintenance and switch over to generator power when necessary.

 

If any of the replies provided the answers you needed. Please do mark those specific replies as a solution so it may help the next person asking the same! 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Moto
Crewman Moto
Crewman

Posted: ‎2025-06-09 12:23 AM

In response to Teken
0 Likes
0
107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-09 12:23 AM

Thanks !

I also had a chance to talk with UPS user. According to him, voltage variation is more criticial compared with frequency variation. Anyway, I think that I could collect necessary information here.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of