APC UPS Data Center & Enterprise Solutions Forum
Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.
Posted: 2022-01-22 11:17 AM
I have a AP9630 that has lost communication to the UPS after and update to the firmware. It's been months since this happened, as I have not been able to shut down the load until now. I have shut down al loads, reset the mgmnt card, and also tried removing it for 30 seconds and then plugging git back in.
UPS Model: SMT2200RM2U
Card Model: AP9630
Attaching info and data, etc.
More info:
Hardware Factory
Model Number
AP9630
Serial Number
ZA1410017745
Hardware Revision
05
Manufacture Date
03/10/2014
MAC Address
00 C0 B7 85 10 3D
Management Uptime
0 Days 0 Hours 1 Minute
Application Module
Name
px2
Version
v6.5.0
Date
Jul 20 2017
Time
17:28:24
APC OS (AOS)
Name
aos
Version
v6.5.0
Date
Jun 9 2017
Time
13:41:00
APC Boot Monitor
Name
bootmon
Version
v1.0.8
Date
Apr 8 2014
Time
10:59:40
Posted: 2022-01-22 11:45 AM
Replying to my own question here...
I updated the firmware to 6.9.6 from here:
That resolved the communications issue.
Posted: 2022-01-22 11:45 AM
Replying to my own question here...
I updated the firmware to 6.9.6 from here:
That resolved the communications issue.
Posted: 2022-01-24 06:13 AM
Hi @daave,
Can I ask where you found the firmware you originally installed - the wrong one?
I ask because you're the second user I've seen install this exact firmware (px2 6.5.0) on a SmartUPS in the space of a week or two, and I'm not a big believer in coincidence - so I'm wondering what's going wrong where that this is showing up as a good search result for the SmartUPS.
You've already found exactly the solution I'd provide as well - I'm just curious if we can tweak something to help people find the right firmware the first time.
Thanks,
Shaun
Posted: 2022-01-24 10:53 PM
Sorry; it was months ago, and I just don't recall. I would have simply come to the SE web site, done a search for my product and downloaded the latest version, which is exactly what I did this time as well.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.