New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Trickle Charger for Spare Batteries
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-2911:21 AM
Trickle Charger for Spare Batteries
We have a SRT10KRMXLT UPS and one external battery pack (SRT192RMBP2). I've ordered a spare set of batteries for keeping on the shelf and I would like to keep them charged up. Does Schneider Electric offer or can you recommend a trickle charger for maintaining a charge on these spare UPS batteries?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-3004:25 AM
There are no trickle chargers sold by APC / Schneider for any UPS.
You can simply insert them into the extended battery pack once a month for a day and than remove marking the date, initial charge / final charge.
From a logistics and maintenance standpoint RBC should be ordered a month in advance of a pending change.
Keeping RBC’s as hot spares is wasteful in terms of storage, finances, and warranty. It defeats the whole purpose of the RBC end of life notification whether via LCD, NMC, NMS, SNMP, SMTP, etc.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-3004:25 AM
There are no trickle chargers sold by APC / Schneider for any UPS.
You can simply insert them into the extended battery pack once a month for a day and than remove marking the date, initial charge / final charge.
From a logistics and maintenance standpoint RBC should be ordered a month in advance of a pending change.
Keeping RBC’s as hot spares is wasteful in terms of storage, finances, and warranty. It defeats the whole purpose of the RBC end of life notification whether via LCD, NMC, NMS, SNMP, SMTP, etc.