Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

The old "UPS: The local network management interface-to-UPS communication not established." error and more

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: The old "UPS: The local network management interface-to-UPS communication not established." error and more
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM

0 Likes
1
392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:43 AM

The old "UPS: The local network management interface-to-UPS communication not established." error and more

This question was originally posted by Evandro on APC forums on 11/28/2013


Hi,

I have an SUA3000RMXL3U-BR (identical to the other model, except for the standard of the output outlets, brazilian-defined).  It's brand new, with 4 months of use.

Recently I installed powerchute (newest version) and connected supplied usb cable. Worked fine. Detected and installed device driver automatically (windows 2008 enterprise server R2), and when I installed powerchute bussiness 3 components, (agent, server, console), it detected correctly my UPS and worked very well.

Suddenly, with no explanation, it lost the communication with the UPS. When I removed and plugged again the usb cable, the infamous message "

One of the USB devices attached to your computer has malfunctioned, and Windows does not recognize it

Tried everything, no success. So I started trying use the AP9630 wich is attached at the rear of the UPS. I update it's firmware, put an ip on it, accessed it fine via web. BUT EVEN NMC2 could communicate with the ups, generating in the logs the message describe in the title of this topic.

So, later, on the server, the message of sucessful recognition of the UPS apperead again, but the powerchute agent (I removed and reinstalled again) could'nt find the UPS as it did before.

Long story short : It appears all communicating capabilites of the UPS has vanished, since either via USB cable using the connector at the rear of the UPS or via NMC2 card, communcation with UPS not happens.

What do you need from me to start troubleshoting my problem ? I tried several solutions for similar problems here, but as far I could see, many people had many particular problems, so despite the fact the problem is a common issue, the solution can vary.

Thank you in advance,

Evandro

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9630
  • communication
  • network_management_card
  • nmc2_communication
  • powerchute_lost_communication
  • ups_communication
  • ups_lost_communication_nmc2
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM

0 Likes
0
392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:43 AM

This reply was originally posted by Evandro on APC forums on 11/29/2013


Guys and girls from tech support from APC, don't bother with my question.

Later I saw other KB here and found the solution.

You can't use BOTH network management AND usb management at same time. Either you disconnect the cable from you UPS NMC, or the USB cable (or serial) from the UPS.

Not both.

After disconnect my usb cable, the communication between NMC2 (ap9630) and the UPS changed to UP and online after an NMC2 reboot.

Thank you,

Evandro

See Answer In Context

Reply
Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM

0 Likes
0
393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:43 AM

This reply was originally posted by Evandro on APC forums on 11/29/2013


Guys and girls from tech support from APC, don't bother with my question.

Later I saw other KB here and found the solution.

You can't use BOTH network management AND usb management at same time. Either you disconnect the cable from you UPS NMC, or the USB cable (or serial) from the UPS.

Not both.

After disconnect my usb cable, the communication between NMC2 (ap9630) and the UPS changed to UP and online after an NMC2 reboot.

Thank you,

Evandro

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc