Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Test e-mail failed; SMTP configuration error on Smart-UPS 5000 with NMC2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Test e-mail failed; SMTP configuration error on Smart-UPS 5000 with NMC2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
robbiethek
robbiethek
Explorer

Posted: ‎2025-02-28 10:10 AM . Last Modified: ‎2025-03-01 03:48 PM

0 Likes
9
5099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-28 10:10 AM . Last Modified: ‎2025-03-01 03:48 PM

Test e-mail failed; SMTP configuration error on Smart-UPS 5000 with NMC2

We have a Smart-UPS 5000 and can't get the email notifications to go out. We have a Linux mail server running Postifx that is in the same subnet so I tried setting the SMTP Server IP and tried both ports 25 and 587. When testing I always get:

Last Test Result
(email redacted) Test e-mail failed; SMTP configuration error.
Last Server Response
No data.

 

I've read the troubleshooting article, as well as this related thread and this one. What else can I check? I made sure firewalld allows the Smart-UPS IP address as well as ports 25 and 587. I tried posting a full tcpdump but it got labeled as the word that rhymes with ham.

 

192.168.1.11. is the mail server and 192.168.1.231 is the Smart UPS 5000. Some examples from tcpdump:

 

14:05:56.543855 IP 192.168.1.11.54530 > 192.168.1.231.http: Flags [S], seq 1935784362, win 29200, options [mss 1460,sackOK,TS val 4103350040 ecr 0,nop,wscale 7], length 0

14:05:56.546389 IP 192.168.1.231.http > 192.168.1.11.54530: Flags [S.], seq 1709129928, ack 1935784363, win 4380, options [mss 1460,nop,wscale 0,nop,nop,sackOK], length 0

14:05:56.546404 IP 192.168.1.11.54530 > 192.168.1.231.http: Flags [.], ack 1, win 229, length 0

14:05:56.546454 IP 192.168.1.11.54530 > 192.168.1.231.http: Flags [P.], seq 1:594, ack 1, win 229, length 593: HTTP: POST /NMC/kBoNgel0R0JdgRZndCLrMg/Forms/emtest1 HTTP/1.1

14:05:57.097070 IP 192.168.1.11 > 192.168.1.231: ICMP host 192.168.1.11 unreachable - admin prohibited, length 60

14:05:57.147846 IP 192.168.1.11.54530 > 192.168.1.231.http: Flags [P.], seq 594:1086, ack 413, win 237, length 492: HTTP: GET /NMC/kBoNgel0R0JdgRZndCLrMg/emtest.htm HTTP/1.1
14:05:57.190049 IP 192.168.1.231.http > 192.168.1.11.54530: Flags [P.], seq 413:867, ack 1086, win 3295, length 454: HTTP: HTTP/1.1 200 OK

14:05:58.076116 IP 192.168.1.231.puppet > 192.168.1.11.submission: Flags [S], seq 2919252718, win 4380, options [mss 1460,nop,wscale 0,nop,nop,sackOK], length 0
14:05:58.076230 IP 192.168.1.11 > 192.168.1.231: ICMP host 192.168.1.11 unreachable - admin prohibited, length 60

14:06:00.076497 IP 192.168.1.231.puppet > 192.168.1.11.submission: Flags [S], seq 2919252718, win 4380, options [mss 1460,nop,wscale 0,nop,nop,sackOK], length 0
14:06:00.076545 IP 192.168.1.11 > 192.168.1.231: ICMP host 192.168.1.11 unreachable - admin prohibited, length 60

14:06:04.076324 IP 192.168.1.231.puppet > 192.168.1.11.submission: Flags [S], seq 2919252718, win 4380, options [mss 1460,nop,wscale 0,nop,nop,sackOK], length 0

  • Tags:
  • 5000
  • email
  • english
  • nmc2
  • notifications
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
Teken
Teken
Champion

Posted: ‎2025-03-02 10:59 PM

0 Likes
6
5096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-02 10:59 PM

What firmware is the NMC 2 running?!? If you’re still on 5.XX / 6.XX firmware you need to upgrade to v7.1.8.

 

Show me the SMTP Server settings and a screen capture of the About tab for the NMC.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

robbiethek
robbiethek
Explorer

Posted: ‎2025-03-03 06:15 AM

In response to Teken
0 Likes
5
5030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-03 06:15 AM

Firmware Revision is 657.19.M

Application Module v7.1.8

 

Screenshot 2025-03-03 at 9.10.05 AM.pngScreenshot 2025-03-03 at 9.10.53 AM.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-03-04 05:26 AM

In response to robbiethek
0 Likes
4
5025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-04 05:26 AM

Sorry can’t see the images you uploaded so please verify it can be seen once loaded to the APC Forum.

 

You can simply write out the settings minus any user details for privacy reasons.

 

In the interim I would suggest you sign up for a throw away email account with Google. Insure you have setup the *Less Secure* Application password for this new email alias.

 

Once setup use Google as the SMTP Server and report back the results.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

robbiethek
robbiethek
Explorer

Posted: ‎2025-03-04 09:39 AM

In response to Teken
0 Likes
1
4997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-04 09:39 AM

the screenshots are there now. This APC does not have external access and the subnet is NAT'ed. But as mentioned we have access to a Postfix server on the same subnet. How else can I troubleshoot?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-03-05 06:51 AM

In response to robbiethek
0 Likes
0
4983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-05 06:51 AM

Sorry can’t see the images at all try another image format and verify it’s viewable on the APC Forum.

 

What other network appliance is on site using this internal method to send mail? Have you used the same SMTP settings and credentials?!?


What are the results using the same on the APC UPS?

 

Questions Ask . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

mikeinnyc
mikeinnyc
Contributor

Posted: ‎2025-03-05 12:41 PM

0 Likes
0
4951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-05 12:41 PM

I've done the legwork for SMTP to work properly.

You can either have any of the following 1,2, or 3



1) An Email alert:

2) An SMS Text:

3) Or Urgent Matters a Phone call:

Or All three at the same time.

 

I'll show you email on here.

 

1) Go to Google and click on your account.

2) Go to Security on the left

3) Go to 2-Step Verification

4) At the Bottom of the page App passwords

To create a new app specific password, type a name for it below.

5) Call It APC or Netbotz or whatever.

6) Copy the password with the spaces don't format it.

----------------------------------------------------------------------------------------------------

E-mail Server Settings
Active Primary DNS Server
192.168.1.1 or the IP address of your Local FIREWALL
Active Secondary DNS Server
1.1.1.1

 

7) Go to APC and login in the GUI

😎 Configuration / Notification / Email / Server

9) SMTP Server is : smtp.gmail.com

Port is 465 - Yes this is correct

Authentication is checked
9) Outgoing Mail Configuration
9) From Address: mike@gmail.com
User Name: Google email mike@gmail.com (Not my real email)
Note: From address and User name are the same working google email address.
Password: Paste the password you generated in google here.
If you messed this up go back to google and delete the APC then recreated it and get a new password.
Copy that password and paste in here and confirm.
Use SSL/TLS: Implicitly
Require CA Root Certificate = blank or unchecked.
 
mikeinnyc_0-1741206779754.png

 

 
 mikeinnyc_1-1741207276916.png

 

Attachments
  • Tags:
  • SMTP Alerts
Reply

Link copied. Please paste this link to share this article on your social media post.

robbiethek
robbiethek
Explorer

Posted: ‎2025-03-10 06:42 AM

0 Likes
0
4841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-10 06:42 AM

None of these are working Google no longer has that password option in security.

 

Screenshot 2025-03-10 at 9.27.38 AM.pngScreenshot 2025-03-10 at 9.39.27 AM.png

 

Screenshot 2025-03-03 at 9.10.05 AM.pngScreenshot 2025-03-03 at 9.10.53 AM.png

Reply

Link copied. Please paste this link to share this article on your social media post.

robbiethek
robbiethek
Explorer

Posted: ‎2025-03-11 10:49 AM

In response to Teken
0 Likes
1
4806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-11 10:49 AM

<<<Sorry can’t see the images you uploaded so please verify it can be seen once loaded to the APC Forum.<<<

 

Try Safari it seems Google Chrome is blocking images in line, here is what Developer Tools shows:

Request URL:
https://community.se.com/skins/images/BF6D159B146D118BE9AA6800BDEB42FC/responsive_peak/images/image_unmoderated.gif
Request Method:
GET
Status Code:
200 OK (from memory cache)
Remote Address:
18.164.96.18:443
Referrer Policy:
strict-origin-when-cross-origin
cache-control:
s-maxage=10
content-length:
986
content-type:
image/gif;charset=UTF-8
date:
Mon, 10 Mar 2025 13:02:20 GMT
expires:
Tue, 10 Mar 2026 13:02:20 GMT
last-modified:
Mon, 10 Mar 2025 13:01:30 GMT
server:
Apache
vary:
Origin
via:
1.1 fa503ecd9278a874859948f3b586c782.cloudfront.net (CloudFront)
x-amz-cf-id:
ubY_r4J7pvutdOqA3CKiZSAkkc5Z-zo3j0biNE-g4s90nW7obsHxLg==
x-amz-cf-pop:
JFK50-P5
x-cache:
Miss from cloudfront
x-content-type-options:
nosniff
referer:
https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/Test-e-mail-failed-SMTP-configuration-error-on-Smart-UPS-5000/m-p/502173
sec-ch-ua:
"Chromium";v="134", "Not:A-Brand";v="24", "Google Chrome";v="134"
sec-ch-ua-mobile:
?0
sec-ch-ua-platform:
"macOS"
user-agent:
Mozilla/5.0 (Macintosh; Intel Mac OS X 10_15_7) AppleWebKit/537.36 (KHTML, like Gecko) Chrome/134.0.0.0 Safari/537.36

 

Reply

Link copied. Please paste this link to share this article on your social media post.

seuser3
seuser3
Explorer

Posted: ‎2025-03-12 07:25 AM

In response to robbiethek
0 Likes
0
4783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-12 07:25 AM

FWIW - I cannot see your images either on Firefox. They show as triangular warning symbols (attaching screenshot) and they all link to (edited to avoid it rendering as an image) https <colon> <slash> <slash> community <dot> se <dot> com/skins/images/A9A96D14CA687CD7FCFDF3B8156C5458/responsive_peak/images/image_unmoderated.gif

 

In looking at your tcpdump results that involve the SMTP server @ 192.168.1.11 you are not able to contact tcp port 587 which implies a firewall on the host and/or some other network restriction (less likely since you note they are on the same subnet) is not configured to allow the connection from the source IP 192.168.1.231. You would need to open that port and confirm the UPS is allowed to connect to it before you will be able to send mail through that route. Once you see a successful connection via tcpdump if it still doesn't work check your SMTP server's syslog to see what postfix is saying and go from there.

 

14:05:57.097070 IP 192.168.1.11 > 192.168.1.231: ICMP host 192.168.1.11 unreachable - admin prohibited, length 60

14:05:58.076116 IP 192.168.1.231.puppet > 192.168.1.11.submission: Flags [S], seq 2919252718, win 4380, options [mss 1460,nop,wscale 0,nop,nop,sackOK], length 0
14:05:58.076230 IP 192.168.1.11 > 192.168.1.231: ICMP host 192.168.1.11 unreachable - admin prohibited, length 60

14:06:00.076497 IP 192.168.1.231.puppet > 192.168.1.11.submission: Flags [S], seq 2919252718, win 4380, options [mss 1460,nop,wscale 0,nop,nop,sackOK], length 0
14:06:00.076545 IP 192.168.1.11 > 192.168.1.231: ICMP host 192.168.1.11 unreachable - admin prohibited, length 60

14:06:04.076324 IP 192.168.1.231.puppet > 192.168.1.11.submission: Flags [S], seq 2919252718, win 4380, options [mss 1460,nop,wscale 0,nop,nop,sackOK], length 0

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore