Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Still confused - Shutdown Server on Battery (PCNS) vs. Low Battery Duration

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Griffey Shoes
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
belred_apc
belred_apc
Cadet

Posted: ‎2021-06-30 11:19 PM

0 Likes
2
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 11:19 PM

Still confused - Shutdown Server on Battery (PCNS) vs. Low Battery Duration

This was originally posted on APC forums on 2/16/2011


I'm sorry...I've read many posts and replies but I'm afraid I'm still confused as to the purpose of these settings.

- In the PCNS client, I have configured the 'UPS: On Battery" event to 'Shut Down System' when the event lasts 300 seconds.
- In the PCNS client, I have Configured Shutdown to turn off the UPS after the shutdown finishes.*

There's also a setting in the NMC where you can configure 'Low Battery Duration'. This is defaulted to two minutes, and I read somewhere that this is used to shutdown ALL clients if they haven't configured any shutdown events. Since my server takes up to 20 minutes to shutdown (large SQL), would it make sense to change this setting to 20 minutes in case the server doesn't shutdown via the timed event? I assume APC can shutdown the server without any additional configuration/scripts, since at this point I'm not using any command files to shutdown services/server. I may choose to add that in later.

*I don't see where you can configure how long the UPS waits AFTER it starts the server shutdown before it will shutdown the UPS, so I am assuming the APC knows that the client has shutdown before proceeding? If not, please explain how this works and if I need to configure this somewhere.

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
seoerming1_apc
Lieutenant JG seoerming1_apc
Lieutenant JG

Posted: ‎2021-06-30 11:19 PM

0 Likes
0
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 11:19 PM

This was originally posted on APC forums on 3/23/2011


"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

See Answer In Context

Reply
Share
Replies 2
belred_apc
belred_apc
Cadet

Posted: ‎2021-06-30 11:19 PM

0 Likes
0
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 11:19 PM

This was originally posted on APC forums on 2/17/2011


Thanks for the explanation...makes sense now.

Reply
Share
seoerming1_apc
Lieutenant JG seoerming1_apc
Lieutenant JG

Posted: ‎2021-06-30 11:19 PM

0 Likes
0
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 11:19 PM

This was originally posted on APC forums on 3/23/2011


"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc