Smart-UPS X3000 repeated failures - Need advice before engaging support again

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X3000 repeated failures - Need advice before engaging support again
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All
Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
GC-IDS
Crewman GC-IDS
Crewman

Posted: ‎2025-01-23 12:17 PM

0 Likes
1
373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-23 12:17 PM

Smart-UPS X3000 repeated failures - Need advice before engaging support again

Hey all.

 

What I'm about to relay here is one of the strangest issues I've dealt with in 20+ years of IT and before I enter the support gauntlet again, I wanted to get a sanity check from the community.

 

We have a client with two Smart-UPS X3000 units of different ages. One's in warranty, one isn't and they both have expansion battery packs. The unit in warranty worked great for a number of months, then started throwing errors.

 

After working with support, they elected to replace the unit. One heavy shipment and installation later and shortly after, the new one started doing the same thing. Another heavy shipment and installation later, things were working well for a time, then we started getting errors that the battery was overheating and not installed properly, despite coming installed in the replacements and being in the same location that was not only properly cooled, but also didn't feel warm even. A battery replacement later and shortly after, the same issue occurred. Another battery replacement later and things worked for about 6 months, and now the errors are back. The older of the two units has worked happily and without issue this entire time.

 

This what shows in the NMC log:

 

 01/13/2025 16:19:57 Device UPS: The internal battery temperature exceeds the critical threshold.
 01/13/2025 16:19:57 Device UPS: At least one faulty battery exists.
 01/13/2025 16:19:57 Device

UPS: The battery is not installed properly.

 

Last occurrence of these errors is the 13th as you see, and they haven't cleared. Prior to this, the errors did occasionally clear, sometimes for days at a time, then they'd return. We wondered if perhaps the expansion unit (which is older and has never been replaced) might be having the issue, but the logs indicate it's the internal battery.

 

I simply cannot believe that the same defect has existed across two UPS and three battery replacements now. I've been at this a long time and have seen some very weird, one in a high number things happen, but this? I just don't buy it. However, I'm at a loss to explain it as nothing else in the environment has changed and the original unit worked for a good while before this happened.

 

I really don't want to have to do another installation of heavy equipment that requires two people just to have this fail yet again. Before I go back into it with support (who I'm sure will just want to send another replacement), has anyone seen this and perhaps has insights into anything we could try to deal with it before then?

 

Thanks all.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
  • errors
  • repeat issue
  • smart-ups
  • x3000
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Spock Teken
Spock

Posted: ‎2025-01-24 05:55 AM

0 Likes
0
352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-24 05:55 AM

You’ll need to provide a lot more detailed information here such as event, data, ups logs.

 

Show me the About information for the UPS / NMC.

 

In the interim show me what the current ambient temperature is in that room compared to the battery temperature from the main system.

 

Disconnect all of the extended battery pack from the main unit. Power down and disconnect all connected loads. Disconnect the internal battery cartridge from the main unit and wait for the system to declare a battery fault. Report back what the system indicates as to the internal battery temperature and write it down.

Next get a fan and place it in front of the battery compartment and let it run. You should be able to see the internal battery temperature drop in Power Chute, NMC, NMS.

 

Report back what the temperature is once stabilized. Upload the data, event, ups logs again once this step has been completed.

 

Expectation is the system will indicate a drop in internal temperature. The battery temperature fault should clear if it doesn’t report this here.

 

Keep in mind if this is a hard fault than you will need to remove AC mains from the wall outlet. Wait 60 seconds than reconnect the AC mains.

 

The system should turn on and later declare a battery missing / disconnected fault. Ignore it and report back what the system indicates as the battery internal temperature.

 

The critical battery temperature fault should be gone now. If not report that information here.

 

Questions Ask . . . 👍

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of