Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Smart UPS RT 8000 XL discharges batteries on Self-Test

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS RT 8000 XL discharges batteries on Self-Test
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
kazuzapt_apc
Crewman kazuzapt_apc
Crewman

Posted: ‎2021-06-29 04:58 AM

0 Likes
3
567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 04:58 AM

Smart UPS RT 8000 XL discharges batteries on Self-Test

This was originally posted on APC forums on 11/29/2012


Good afternoon all

I have in my facilities the above UPS and got indication to replace batteries a few weeks ago..

Replaced batteries (all four of them) with original RBC44 (2 of them) and put it into production

Now after leaving the unit charge batteries for 2 days now, i get indication that batteries are 100% charged, 217VDC on them, but as soon as I perform a self test, i get events that batteries are too low to support the load (when actually there is NO LOAD) and charge percentile drops to 14% and increments there on to 100% in a few hours. Repeating the self-test again produces the same result in a infinite loop

I have no events regarding any failure whatsowever

Am I missing something, or do I have a problem in my unit?


Thanks for any help regarding this issue

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
kazuzapt_apc
Crewman kazuzapt_apc
Crewman

Posted: ‎2021-06-29 04:58 AM

0 Likes
1
570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 04:58 AM

This was originally posted on APC forums on 12/3/2012


Thanks for all your input i picKed a winna

However that did not solve my problema. Neither calibration nor discharging with a 30% load until exhaustion

Had to remove the 9631 card and entered via serial port into SM where I could reset the UPS to state 8C

After comproving correct functioning, inserted network card again and everything is working now

Thanks for your help

See Answer In Context

Reply
Share
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:58 AM

0 Likes
0
570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 04:58 AM

This reply was originally posted by Angela on APC forums on 11/29/2012


how much battery runtime does the UPS report? i am assuming it is because it is within two minutes of the low battery signaling time which defaults to two minutes.

if these are geniune replacement batteries, i suspect you just need a runtime calibration to tell the UPS you have new batteries. you should generally do this with a load on the UPS of at least 30% and make sure it does not fluctuate. the management card installed can execute the calibration for you or you can do it manually if you'd like and remove power from the UPS and let it turn off completely and charge back up. if you do the calibration via the management card, it will discharge the UPS to about 10-15% and then charge back up incase you don't want the attached load to shutdown hard.

Reply
Share
kazuzapt_apc
Crewman kazuzapt_apc
Crewman

Posted: ‎2021-06-29 04:58 AM

0 Likes
1
571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 04:58 AM

This was originally posted on APC forums on 12/3/2012


Thanks for all your input i picKed a winna

However that did not solve my problema. Neither calibration nor discharging with a 30% load until exhaustion

Had to remove the 9631 card and entered via serial port into SM where I could reset the UPS to state 8C

After comproving correct functioning, inserted network card again and everything is working now

Thanks for your help

Reply
Share
apatel777
apatel777
Cadet

Posted: ‎2022-03-13 10:39 AM

In response to kazuzapt_apc
0 Likes
0
437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-03-13 10:39 AM

I have the same challenge after battery replacement, shows discharged battery warning, 0 mins runtime and not calibrating.

 

With regards to this solution - Had to remove the 9631 card and entered via serial port into SM where I could reset the UPS to state 8C

 

Can you advise what you mean by state 8C, is this a simple process, does it require everything to be unplugged from UPS?

 

Thanks

  • Tags:
  • english
Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc