We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:05 AM
The UPS has 3.5 years. Last week there was a power outage for a few minutes and the UPS acted as if there were no batteries: the computers were turned off ...
Before the power came back I did some testing. The only things I could do: push the button to turn off and all LEDs turned off. After I pressed the power button, releasing the second beep and there was a sequence of LED lighting and deleting and relays noises, ending with the Fault LED on.
At my command it starts the self-test or calibration, but soon abandons any of the two.
As the batteries may have been old, I decided to change them. The same thing happens. I tried to calibrate with more than 30% load and the reactions are always the same: Relay noises, LEDs in a sequence, ending with the fault LED on.
I put below state data and event log:
Last Diagnostic Results
Self-test Result No Result Available
Self-test Date Janeiro 2015
Runtime Calibration Result Cancelled
Runtime Calibration Date Janeiro 2015
Bypass Status
Current Status Not In Bypass
UPS System Parameters Status
Device Status On line
UPS Load 0,0 %
Runtime Remaining 150 Minutes
Internal Temperature 29,6 °C / 85,3 °F
Load Power 0 % VA
Load Current 0 A
Power Status
Line Voltage 120,9 VAC
Output Voltage 120,2 VAC
Output Frequency 60,0 Hz
Battery Status
Battery Charge 100,0 %
Battery Voltage 54,3 VDC
Total Battery Packs 1
27/01/15 09:43:32 Bypass Ended
27/01/15 09:43:24 Self Test Initiated
27/01/15 09:43:20 UPS In Bypass Due To Internal Fault
27/01/15 09:43:20 Calibration Cancelled
27/01/15 09:43:16 Calibration Started
27/01/15 09:28:34 Bypass Ended
27/01/15 09:28:26 Self Test Initiated
27/01/15 09:28:22 UPS In Bypass Due To Internal Fault
27/01/15 09:28:22 Calibration Cancelled
27/01/15 09:28:17 Calibration Started
26/01/15 19:19:07 Bypass Ended
26/01/15 19:18:55 UPS In Bypass Due To Internal Fault
26/01/15 19:18:55 Self Test Initiated
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:05 AM
It sounds like your UPS was likely in bypass operation when you had the power outage. It appears to be in bypass (operating on utility power) because of an internal fault. Based on what you describe and what I see in the log, I think your UPS likely requires some repair (or replacement) depending on where you're located and its warranty status.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:32 PM . Last Modified: 2024-03-19 12:05 AM
It sounds like your UPS was likely in bypass operation when you had the power outage. It appears to be in bypass (operating on utility power) because of an internal fault. Based on what you describe and what I see in the log, I think your UPS likely requires some repair (or replacement) depending on where you're located and its warranty status.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of