New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Smart-UPS On-Line SRTL 3000VA
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-3101:58 AM
Smart-UPS On-Line SRTL 3000VA
Hi,
I have a brand new set of SRTL3000RM4UXLI-NC which consists of Power module (SRT3000UXI-NCLI) & XBP48RM2U-LI (Lithium battery pack)
First Issue: Right out of the box, I probed the XBP DC cable and DC receptacle but to my supprise I got only 0.1+ VDC. Is this normal ?
Regardless, I carried on with the installation as per the manual and connected the Battery cable, DB15 comm. cable & ground cable between UPS & XBP with the hope that the UPS would somehow trigger the XBP to switch ON. Due to the reactive nature of Lithium cells I decided to cold start the UPS without mains input just to be safe.
2nd Issue: As expected, UPS doesn't startup. Not a single beep and display panel doesn't illuminate. Is this a sign of a defective XBP48RM2U-LI ?
Unlike the Lead-Acid models, there used to be a RBC plug at the front side which act as a safety disconnect but on this Lithium unit, there are no switch or disconnects present.
Finally, is it safe to plug in AC mains and let it charge up ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-3105:16 AM
Plug the system into AC Mains and power up the system and report back the outcome.
Along with the status of the rear LED on the external battery pack.
All lithium cells incorporate a BCM as such it acts like a switch thus you would measure no voltage because the BCM hasn’t turned on to allow DC voltage to flow.
Im not sure why you / your company decided to purchase this specific model?!?
Given it’s scheduled to be EOL and discontinued?? Besides the fact this specific product line was a complete dud since launch and has a very high failure rate hence why it’s been abandoned and EOL. 🤦♂️
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-0208:09 PM
Hi Teken,
Thanks for the info. I will try powering the unit with AC Mains and report back the outcome.
Frankly, I had no knowledge of this model (and some SRTL models) are scheduled to be EOL until you brought it up. Then as I dug further, at least in Asia Pacific SRTL (Lithium based) models are "still commercialised".