Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Smart-UPS 600 (2G, from 1994) Feature Programming

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 600 (2G, from 1994) Feature Programming
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5060
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-12 07:51 AM

0 Likes
2
3054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-12 07:51 AM

Smart-UPS 600 (2G, from 1994) Feature Programming

Another oldie but a goodie...discovered brand new in box, in fact! A set of new batteries and some diddling around got it running nicely again. (Model # AP600, S/N: S94062924341)

The user's manual for this unit indicates that various settings can be adjusted in software such as Powerchute Plus or software for DOS known as Power Doctor. In particular, I'd like to turn off the beeper at all times, and the manual clearly indicates that this can be done via software.

PowerChute Plus can communicate with the UPS and display some statistical information (load percentage, line voltage, etc.) , but shows all such settings as being unavailable. Communicating directly via UPSlink in a terminal emulator and trying to set the beeper to its disabled state results in a "NO" response. The same is true of other parameters that are claimed to be adjustable in the unit's manual.

Is there perhaps an earlier revision of UPSlink with different commands, or might I be able to secure an older version of PowerChute Plus (maybe even Power Doctor for DOS, if it can be found) software to communicate with this unit? (It seems like a crime to descend upon it with a soldering iron just to turn the beeper off, so I hope it doesn't come to that.)

I did not receive any software or communication cable with the unit, and it's unclear if such was in the box originally. I'm inclined to think it was not. Communications were performed with a 940-0024C cable.

 

Smart-UPS 600 2G

(Larger version here. - 360 KB)

I would be greatly appreciative for any help at all. smile

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 1994
  • 2g
  • 600
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-06 03:27 AM

0 Likes
0
3054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-06 03:27 AM

A bit late probably, but in order to be able to modify the settings of a 2nd gen. APC Smart UPS, you need to flip all 4 of the DIP switches to the ON position at the back of the unit. This allows programming mode. You need to set the values modified by these switches in software in order to compensate against the fact that they have to be in the on position to program the unit (eg. output voltage, audible alarm operation, sensitivity...etc). Important: software settings are kept only as long as these switches are left in the on position. A standard 940-0024C cable can be used for communications. These units use an earlier version of the UPSLink protocol, so some commands which are available on 3G models will not work here, and some functions have to be triggered differently in comparison to 3G units (eg. turn on command while unit is offline (due to no RS232 communication is possible when 2nd gen. units are offline), ups capability string and query of some register values are not supported...adjustment of battery constant is also different, see procedure here: http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/11779/second-gen-smart-ups-pr...)

Second generation models were made from 1993-1997, but there are some older (first generation) models made 1990-1992 which support even less commands of UPSLink protocol. You can determine UPSLink version from the response to the capital V command (second character, eg. response 6TI means a Smart UPS 600 with UPSLink version T, which is the newest of the second generation models AFAIK. The earliest made unit I've seen so far supporting the V command (and still functioning ๐Ÿ˜„ ) is a 1st gen. Smart UPS 400 made in 1991 with UPSLink version C)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-06 03:27 AM

0 Likes
0
3054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-06 03:27 AM

*bump* Anyone out there with some ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-06 03:27 AM

0 Likes
0
3054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 10:57 PM . Last Modified: โ€Ž2024-03-06 03:27 AM

A bit late probably, but in order to be able to modify the settings of a 2nd gen. APC Smart UPS, you need to flip all 4 of the DIP switches to the ON position at the back of the unit. This allows programming mode. You need to set the values modified by these switches in software in order to compensate against the fact that they have to be in the on position to program the unit (eg. output voltage, audible alarm operation, sensitivity...etc). Important: software settings are kept only as long as these switches are left in the on position. A standard 940-0024C cable can be used for communications. These units use an earlier version of the UPSLink protocol, so some commands which are available on 3G models will not work here, and some functions have to be triggered differently in comparison to 3G units (eg. turn on command while unit is offline (due to no RS232 communication is possible when 2nd gen. units are offline), ups capability string and query of some register values are not supported...adjustment of battery constant is also different, see procedure here: http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/11779/second-gen-smart-ups-pr...)

Second generation models were made from 1993-1997, but there are some older (first generation) models made 1990-1992 which support even less commands of UPSLink protocol. You can determine UPSLink version from the response to the capital V command (second character, eg. response 6TI means a Smart UPS 600 with UPSLink version T, which is the newest of the second generation models AFAIK. The earliest made unit I've seen so far supporting the V command (and still functioning ๐Ÿ˜„ ) is a 1st gen. Smart UPS 400 made in 1991 with UPSLink version C)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore