Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Smart UPS 1400XL - Any way to restore after control-y command

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Smart UPS 1400XL - Any way to restore after control-y command
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
brblack_apc
Crewman brblack_apc
Crewman

Posted: ‎2021-07-07 10:29 PM

0 Likes
5
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 10:29 PM

Smart UPS 1400XL - Any way to restore after control-y command

This was originally posted on APC forums on 5/5/2015


Is there any way to restore after I accidently hit control-y while in the console.  It appears that this command has pretty much wiped all information from the prom. Even checking the model now responds back with the model being a 450.

Thanks for any bright ideas.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
brblack_apc
Crewman brblack_apc
Crewman

Posted: ‎2021-07-07 10:30 PM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 10:30 PM

This was originally posted on APC forums on 5/9/2015


Thank you for the link. It appears that the first one did the trick. I was able to reset the firmware to the correct version and also had to set the line voltage an load. So far it looks like everything is up and running again, but I'll do a little testing to make sure everything is working.

See Answer In Context

Reply
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:29 PM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 10:29 PM

This reply was originally posted by Angela on APC forums on 5/6/2015


Hi Brian,

This is not field recoverable unfortunately..Ctrl + y does wipe the EEPROM when you're in programming mode. Programming mode was only originally intended for APC use and requires a special timing sequence to gain access to in an effort to prevent a user or program from accidently doing these types of commands when trying to read status information from the UPS.

Reply
kssilence_apc
Ensign kssilence_apc
Ensign

Posted: ‎2021-07-07 10:29 PM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 10:29 PM

This was originally posted on APC forums on 5/6/2015


Brian, Im pretty sure many if not all of the Smart UPS's have their eeprom chip in a socket on the mainboard / "brainboard" rather than being soldered in, i know my 3000XL Modular does, and im also sure my 2200XL Rack mount does as well, quite possibly you could try to get a dead or functioning unit of the same make thats cheap and just swap the eeproms, or if you have access to an eeprom reader / programmer you could dump the good eeprom to file, verify it atleast twice against the eeprom, then program the "wiped" eeprom.

Are you able to change anything in the eeprom over serial still in programming mode? - Alex.

- Alex.

Reply
brblack_apc
Crewman brblack_apc
Crewman

Posted: ‎2021-07-07 10:29 PM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 10:29 PM

This was originally posted on APC forums on 5/6/2015


I do have a second UPS of the same model.  I did open the case and found the chip in socket, so it sounds like I might have a chance. As far a the reader/programmer, I do not have access to one (also checked a few local computer shops to no avail). I have not tried to change anything in the eeprom after the mistake, but I was able to still issue commands and received responses to it.  If you have any suggestions/recomendations about a cheap programmer I'm all ears. I know at this point I would like to try to salvage it, but I do not want to risk swapping the eeproms from one to the other to test it out in fear of loosing the second ups.

Reply
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-07 10:30 PM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 10:30 PM

This was originally posted on APC forums on 5/8/2015


You might be able to copy values from the good unit's EEPROM using the command interface. See:

http://blog.inceweb.com/adrian/2014/05/24/programming-the-apc-smart-ups-700/

and

http://osdir.com/ml/monitoring.nut.user/2007-01/msg00120.html

Reply
brblack_apc
Crewman brblack_apc
Crewman

Posted: ‎2021-07-07 10:30 PM

0 Likes
0
371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-07 10:30 PM

This was originally posted on APC forums on 5/9/2015


Thank you for the link. It appears that the first one did the trick. I was able to reset the firmware to the correct version and also had to set the line voltage an load. So far it looks like everything is up and running again, but I'll do a little testing to make sure everything is working.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc