Servers not starting up automatically after power restore

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
MKMaduro_apc
Ensign
Ensign
0 Likes
1
171

Servers not starting up automatically after power restore

This was originally posted on APC forums on 12/7/2015


I have two servers who are connected to two different APC Smart-ups. Problem that I have is that neither server starts automatically after power restore when a power failure has happen.

Can someone tell me what I am doing wrong that the servers does not start automatically after power restore?

Servers

Connected to UPS

HP Proliant ML370 G5

APC Smart-UPS 2200

HP Proliant ML350p Gen8

APC Smart-UPS 1500

 

Basic settings both UPS

Time required for shutdown sequence

12 minutes

Low battery signal

8 minutes

OS shutdown duration

10:30 minutes

OS shutdown type

shutdown

Enable OS reboot

Yes

UPS turn on battery capacity

30%

UPS turn on delay

1 minutes

 

Thanks


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
172

Re: Servers not starting up automatically after power restore

This reply was originally posted by Bill on APC forums on 12/7/2015


Hi,

You need to set OS to turn on when AC is restored in the BIOS of the computers. We have Kbase FA159550 "Computer will not automatically reboot after UPS has shutdown and restarted" that should help with this issue. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
173

Re: Servers not starting up automatically after power restore

This reply was originally posted by Bill on APC forums on 12/7/2015


Hi,

You need to set OS to turn on when AC is restored in the BIOS of the computers. We have Kbase FA159550 "Computer will not automatically reboot after UPS has shutdown and restarted" that should help with this issue.