New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Safe upgrade path for AP9630 (HW 05) from v5.1.6 to v7.2.2?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phraseβUse quotes " "(e.g., "error 404")
WildcardβUse * for partial words(e.g., build*, *tion)
AND / ORβCombine keywords(e.g., login AND error, login OR signβin)
Keep it shortβUse 2β3 relevant words, not full sentences
FiltersβNarrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-10-2011:21 AM
Safe upgrade path for AP9630 (HW 05) from v5.1.6 to v7.2.2?
Hi everyone,
I need to upgrade an AP9630 NMC2 (HW 05) inside a Smart-UPS X 1000 (SUMX). It currently runs v5.1.6 with bootmon v1.0.2.
I will use FTP to manually flash the .bin files using Linux. I have sourced the following intermediate versions: v5.1.7, v6.0.6, v6.2.0, and v7.2.2.
I noticed that v6.0.6 still uses bootmon v1.0.2, while v6.2.0 jumps to v1.0.8.
What is the safest stepping-stone order to prevent bricking the card? Do I need another v6.x version (like v6.9.6) before moving to v7.2.2?
At each intermediate step, do I flash bootmon.bin first or aos.bin first?
Will the UPS drop the load or power-cycle the connected outputs during the firmware update of the NMC2 card? I have a live server attached that shall stay powered
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-10-2302:59 AM
1. Technically APC indicates you may upgrade from any firmware version without using a staged upgrade path.
Real world, you should upgrade from 5.XX -> 6.XX -> 7.XX
2. This should be done using a Windows computer system and the NMC configured to allow FTP. Launch the firmware upgrade wizard as an Administrator. Enter the NMC credentials / IP Address and select FTP and do (NOT) save logs then hit continue. Once the upgrade pop up message appears wait another ten seconds before closing the application.
3. Upgrading the NMC Firmware has no impact on the operation of the UPS or outputs.