SUA3000RMI2U Wont Turn On

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: SUA3000RMI2U Wont Turn On
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
JCUPS
Crewman JCUPS
Crewman

Posted: ‎2025-05-02 01:56 AM . Last Modified: ‎2025-05-02 03:18 AM

0 Likes
6
254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-02 01:56 AM . Last Modified: ‎2025-05-02 03:18 AM

SUA3000RMI2U Wont Turn On

Hi all

 

I have just got a SUA3000RMI2U and purchased new battery's for it and get 50+ volts from them currently.

When I try to switch it on I get a blip sound and nothing else no LEDs etc.. Power is getting to the main board but I cannot locate any Schematics for it to troubleshoot further

I know it's an old unit but you just work with what you have.

Can anyone suggest any possible known issues or components on these that can fail easily I could look too?

 

Regards

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Spock Teken
Spock

Posted: ‎2025-05-07 04:26 AM

In response to JCUPS
0 Likes
0
141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-07 04:26 AM

This really comes down to how much time you want to invest into this very old legacy device. 

As your unit is 18 years old and that specific model has numerous problems. Your options are to fault find every common failed component such as capacitors, relays, fuse, power transistor etc.

 

Other options are to use the APC Trade-UPS program to offset the cost on a new system. Purchase a refurbished unit from any of the third party sellers.

 

Lastly, buy a used system on eBay but upgrade to a SRT, SMX, SMT with a newer year and the ability to upgrade the UPS firmware offering a LCD Menu and more features.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Teken
Spock Teken
Spock

Posted: ‎2025-05-05 07:09 AM

0 Likes
0
239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-05 07:09 AM

What is the serial number of this unit you’re talking about?


The useable service life depending upon model and production year is 7-10 years.

 

https://www.apc.com/us/en/faqs/FAQ000265093/

 

Connect the system to a computer running APC Power Chute Software or 3rd party like: APCUPSD / NUT.

 

Call out the active faults / errors present. If the system has a NMC installed upload the following logs for review: Event, Data, UPS.

 

Show me a photo of the LED display while the system is connected to AC Mains.


Take a video of you turning the system on and focus on the LED display than provide a link to view the same.

 

Next, take a True RMS Multimeter and measure the output outlets and report the AC value. Follow with setting your meter to DC volts and measure the voltage at the battery terminals while connected to the system.

 

Disconnect the battery terminals and measure just the output from the systems charging cable and report back the value.

 

Show me a photo of the rear of the system. On the rear of the unit is a breaker whether it be a button / switch push / toggle it a few times.

 

If the system has an EPO terminal block insure it’s (NOT) connected to anything and remove the phoenix connector if present.

 

Cold Start: Insure the battery cartridge is fully charged before proceeding. Follow the steps on page 12 to initiate a cold start of the system and report back the results:

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_ASTE-6Z8LLW_EN&p_enDocType=User+guide&p_...

Questions Ask . . . 👍

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JCUPS
Crewman JCUPS
Crewman

Posted: ‎2025-05-05 10:20 AM

0 Likes
1
211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-05 10:20 AM

Hi thanks for the reply SN is JS0708008666

When the battery is connected there is 51.8V to the board. Connect the mains which also arrives at the board.

The unit doesn't do anything apart from a quiet blip. No LEDs on the front control panel at all.

I am assuming there is a faulty component on the board but never really had any exposure to UPS boards.

 

Regards

Christopher

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-05-06 06:08 AM

In response to JCUPS
0 Likes
0
205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 06:08 AM

What are the answers to the other questions?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

JCUPS
Crewman JCUPS
Crewman

Posted: ‎2025-05-06 11:10 AM

0 Likes
0
157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 11:10 AM

Hi

I can't answer the other questions as the unit will not power on so the management card isn't live and I cannot get the PC to talk to it.

Reply

Link copied. Please paste this link to share this article on your social media post.

JCUPS
Crewman JCUPS
Crewman

Posted: ‎2025-05-07 01:35 AM

0 Likes
1
157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-07 01:35 AM

Connect the system to a computer running APC Power Chute Software or 3rd party like: APCUPSD / NUT.

It's connected but no communication at all

Call out the active faults / errors present. If the system has a NMC installed upload the following logs for review: Event, Data, UPS.

No faults as there is no connection

Show me a photo of the LED display while the system is connected to AC Mains.

As per the attched
Take a video of you turning the system on and focus on the LED display than provide a link to view the same.

There is no LED screen

Next, take a True RMS Multimeter and measure the output outlets and report the AC value. Follow with setting your meter to DC volts and measure the voltage at the battery terminals while connected to the system.

There is no output voltage

Disconnect the battery terminals and measure just the output from the systems charging cable and report back the value.

0

Show me a photo of the rear of the system. On the rear of the unit is a breaker whether it be a button / switch push / toggle it a few times.

As attached, pressed the breaker but it is already in

If the system has an EPO terminal block insure it’s (NOT) connected to anything and remove the phoenix connector if present.

Nothing connected to it

Cold Start: Insure the battery cartridge is fully charged before proceeding. Follow the steps on page 12 to initiate a cold start of the system and report back the results:

It does 1 very quiet blip and the second press for 3 seconds doesn't do anything

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-05-07 04:26 AM

In response to JCUPS
0 Likes
0
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-07 04:26 AM

This really comes down to how much time you want to invest into this very old legacy device. 

As your unit is 18 years old and that specific model has numerous problems. Your options are to fault find every common failed component such as capacitors, relays, fuse, power transistor etc.

 

Other options are to use the APC Trade-UPS program to offset the cost on a new system. Purchase a refurbished unit from any of the third party sellers.

 

Lastly, buy a used system on eBay but upgrade to a SRT, SMX, SMT with a newer year and the ability to upgrade the UPS firmware offering a LCD Menu and more features.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of