Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

SU2200RMXL3U/SU3000RMXL3U with SUA48RMXLBP3U batt. pack?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU2200RMXL3U/SU3000RMXL3U with SUA48RMXLBP3U batt. pack?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
DJRCB_apc
DJRCB_apc
Cadet

Posted: ‎2021-06-30 10:39 PM

0 Likes
4
255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 10:39 PM

SU2200RMXL3U/SU3000RMXL3U with SUA48RMXLBP3U batt. pack?

This was originally posted on APC forums on 1/22/2016


hey guys,

is it at all possible to use the SUA48RMXLBP3U on an older SU2200RMXL3U/SU3000RMXL3U UPS unit? if not, how come and is there a work around? 

thank you for the help!

cheers

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • su2200rmxl3u
  • su3000rmxl3u
  • sua48rmxlbp3u
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-30 10:39 PM

0 Likes
0
255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 10:39 PM

This was originally posted on APC forums on 1/23/2016


If I recall properly, the SU and SUA units in the VA range you are dealing with are both 48 volt DC units and both use "blue Andersons" (designated for nominal 48 volt DC use by Anderson and adopted by APC).  However, I believe the SU/SUA units use different buss set ups and the "blues" are different amperes rating (to the best of my memory - I don't have both units in front of me) and therefore don't connect.

IMO, if you are careful about two things - 1.  Compatible connectors that match the amperes required are utilized and 2.  You set the charging circuit of your UPS for the correct number of actual battery packs, you should be OK.  Be super careful in causing any mismatching any of these connectors as both the nominal voltage AND amperages must be proper.  

BTW, I know that the battery trays are NOT compatible in the SU48 and SUA48 units.

See Answer In Context

Reply
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:39 PM

0 Likes
0
255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 10:39 PM

This reply was originally posted by Joe on APC forums on 1/22/2016


As far as I could determine from APC's website, it looks like the SUA48RMXLBP3U uses two (2) RBC27 batteries.  It also appears that the SU2200RMXL3U uses an RBC27 as well.

Do you desire to replace batteries or are you moving them around from unit to unit?

Reply
DJRCB_apc
DJRCB_apc
Cadet

Posted: ‎2021-06-30 10:39 PM

0 Likes
0
255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 10:39 PM

This was originally posted on APC forums on 1/22/2016


im looking to extend the run time of my current UPS(s) SU2200RMXL3U/SU3000RMXL3U. The battery pack used for the  model of UPS i currently have is discontinued (SU48RMXLBP3U).  So i was hoping to be able to use the SUA48RMXLBP3U battery pack on my UPS to extend the run time. 

regards

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:39 PM

0 Likes
0
255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 10:39 PM

This reply was originally posted by Joe on APC forums on 1/23/2016


There are a couple of used SU48RMXLBP3U units on eBay, some with new batteries but, other than that, your question is "above my pay grade" and I am unable to help much at all.

Good luck!

Reply
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-30 10:39 PM

0 Likes
0
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 10:39 PM

This was originally posted on APC forums on 1/23/2016


If I recall properly, the SU and SUA units in the VA range you are dealing with are both 48 volt DC units and both use "blue Andersons" (designated for nominal 48 volt DC use by Anderson and adopted by APC).  However, I believe the SU/SUA units use different buss set ups and the "blues" are different amperes rating (to the best of my memory - I don't have both units in front of me) and therefore don't connect.

IMO, if you are careful about two things - 1.  Compatible connectors that match the amperes required are utilized and 2.  You set the charging circuit of your UPS for the correct number of actual battery packs, you should be OK.  Be super careful in causing any mismatching any of these connectors as both the nominal voltage AND amperages must be proper.  

BTW, I know that the battery trays are NOT compatible in the SU48 and SUA48 units.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc