Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Removing RBC43 from SMT3000RM2UC

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Removing RBC43 from SMT3000RM2UC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
162
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BobO
BobO
Explorer

Posted: ‎2026-08-02 10:28 AM

1 Like
5
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-02 10:28 AM

Removing RBC43 from SMT3000RM2UC

I purchased a replacement RBC-43 for my SMT3000RM2UC.  After unplugging the power connector and removing the 3 screws holding the RBC-43 in the unit, I pulled on the lip to remove the battery and it's stuck.  Stuck to the point that it feels like there could be a 4th screw holding it in somewhere.  Should it be that difficult to slide the battery out of the unit?  Could the battery pack have swelled inside the case to the point where it's no longer removeable?  Is there a way to troubleshoot that specific idea?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2026-08-03 04:18 AM

1 Like
2
181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-03 04:18 AM

There are only three retaining screws that hold the RBC in place. In some instances turning the unit over (upside) down may help eject the RBC.

 

On some older RBC modules there is a very thin lip. If present it requires the user to push the RBC to the right while pulling the cartridge out.

 

Essentially you’re going to wiggle it back & forth while pulling out.

 

If you suspect the RBC is swollen you’ll need to remove the top cover. Once removed you’ll be able to confirm the blockage is a swollen cell(s).

 

Depending upon how deformed the RBC is. The only solution is to bend the opening of the frame a little to allow the RBC to clear the housing.

 

You can then bend the front frame / lip back down.

 

Questions Ask . . . 👍

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Teken
Teken
Champion

Posted: ‎2026-08-03 04:18 AM

1 Like
2
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-03 04:18 AM

There are only three retaining screws that hold the RBC in place. In some instances turning the unit over (upside) down may help eject the RBC.

 

On some older RBC modules there is a very thin lip. If present it requires the user to push the RBC to the right while pulling the cartridge out.

 

Essentially you’re going to wiggle it back & forth while pulling out.

 

If you suspect the RBC is swollen you’ll need to remove the top cover. Once removed you’ll be able to confirm the blockage is a swollen cell(s).

 

Depending upon how deformed the RBC is. The only solution is to bend the opening of the frame a little to allow the RBC to clear the housing.

 

You can then bend the front frame / lip back down.

 

Questions Ask . . . 👍

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BobO
BobO
Explorer

Posted: ‎2026-08-04 11:02 AM

In response to Teken
0 Likes
1
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-04 11:02 AM

The wiggle led to the understanding that there are some notches on the bottom of the RBC that require the RBC to be lifted up slightly to remove from the UPS.  Appreciate the help @Teken!!

Reply

Link copied. Please paste this link to share this article on your social media post.

JamesOConnor
JamesOConnor
Contributor

Posted: ‎2026-08-04 11:18 AM

0 Likes
1
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-04 11:18 AM

Teken is spot on regarding the high probability of swollen battery cells causing the blockage.

 

Before you attempt to force the cartridge out or remove the top cover, please prioritize your physical safety. It is highly recommended to wear a face shield and heavy protective gloves when disassembling a UPS containing swollen batteries. These cells are under physical pressure, and exposing the internal compartment carries a risk of chemical leaks or sudden physical hazards.

 

If wiggling the cartridge does not release the friction hold, powering down the connected load, un-racking the UPS, and removing the top cover is typically the safest approach. This allows you to push the battery out from the rear rather than pulling it from the front.

 

Once the old battery is removed, it is crucial to evaluate a few items before installing the replacement RBC-43:

 

1. Inspect the Chassis and Components Swollen batteries exert tremendous physical pressure on the internals of a UPS. Carefully check the internal rails, the main control board, and all visible connections for physical deformation, stress cracks, or leaked battery acid. Running a new battery cartridge in a compromised chassis introduces significant operational risk.

 

2. Evaluate the Operating Environment Review the ambient temperature surrounding the UPS unit. Heat is the primary catalyst for VRLA battery swelling. As a general guideline, every 15-degree Fahrenheit increase above an ambient 77 degrees Fahrenheit reduces the expected life of a VRLA battery by approximately 50 percent. Ensure the rack has adequate ventilation and cooling to protect your new battery investment.

 

3. Verify the Age of the UPS Check the serial number on the unit to determine if the chassis itself is approaching the end of its reliable lifecycle. The first two numbers following the prefix letters represent the year of manufacture, and the subsequent two numbers indicate the week. For example, a serial number beginning with AS1623 was manufactured in the 23rd week of 2016.

 

If the UPS serial number indicates a year of 16 (2016) or older, it is time to seriously consider replacing the entire UPS rather than investing in a new battery. Aging internal components significantly increase the risk of unexpected power failures or load drops.


James OConnor
Strategic IT Advisor
Hypertec Solutions Partner | hypertecsp.com
D:(480) 626-9010 | W: 1.866.787.0426 x4202 |
E: joconnor@hypertec.com
8655 E Via De Ventura, Ste. G161, Scottsdale, AZ 85258
Free Book: Hyper-Power: https://tinyurl.com/Hyper-Power
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-08-05 04:33 AM

In response to BobO
0 Likes
0
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-05 04:33 AM

Great to hear the problem was solved.

 

Rock On . . . 🤟

Reply

Link copied. Please paste this link to share this article on your social media post.

BobO
BobO
Explorer

Posted: ‎2026-08-07 12:19 PM

In response to JamesOConnor
0 Likes
0
39
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-07 12:19 PM

@JamesOConnor  thanks for the reply.  Those are all great tips and I especially appreciate the quick education on understanding the manufacture date from the serial number.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore