Greetings
I have an APC SCL500RM1UNC Smart-UPS with an integral ON-1571 network management card. I tried upgrading the ON-1571's firmware to 2.5.3.2 but the firmware upgrade utility stopped with the following error:
[05/05/2025 11:33:38] NMC Firmware Update Utility v1.0.4 initialized.
[05/05/2025 11:33:54] Downloading and verifying configuration file from 10.***.***.***, please wait...
[05/05/2025 11:33:55] Firmware distribution does not match target device platform; this could be due to a corrupt distribution.
[05/05/2025 11:33:55] Uploading firmware file 1 of 1: Firmware Image to 10.***.***.***, please wait...
[05/05/2025 11:33:55] Unable to update device 10.***.***.*** with Firmware Image; stopping all further processing of this device!
I can still SSH into the card. Here's the About info from that:
apc>about
E000: Success
Hardware Factory
---------------
Model Number: 0N-1571
Serial Number: 5A2429T34902
Hardware Revision: 3
Manufacture Date: 07/17/2024
MAC Address: 28 29 86 A2 B1 87
Management Uptime: 0 Days 1 Hour 9 Minutes
Application Module
---------------
Name: sucan
Version: v2.5.3.2
Date: Oct 03 2024
Time: 14:54:02
APC OS(AOS)
---------------
Name: aos
Version: v2.5.3.2
Date: Oct 03 2024
Time: 14:54:02
APC Boot Monitor
---------------
Name: boot
Version: v1.5.4.1
Date: Jun 4 2024
Time: 16:20:19
apc>
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-06 01:02 PM
Solved the issue by
SSH into NMC
Enabling ftp on NMC
Using ftp to put
apc_hw21_su_2-5-4-4.nmc3
onto the ON-1571 NMC. After rebooting the NMC, I was then able to successfully run the v2.5.4.4 Firmware Update Utility. The key is that this model ON-1571 NMC is only compatible with _su_ firmware. I had tried to upgrade to a _sucan_ version and that's what caused the corruption initially.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-06 10:41 AM
Based only on the information you have provided it sounds like you installed the wrong NMC firmware version.
Depending upon when the unit was produced / purchased the system could have had a NMC 2 vs NMC 3.
The 2.5.X.X branch is for the current NMC 3. The 7.X.X branch is for the legacy end of life NMC 2.
You’ll need to identify which embedded NMC is on board the unit. Worst case you can try uploading the latest NMC 2 7.2.0 firmware branch and report back the results.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-06 01:02 PM
Solved the issue by
SSH into NMC
Enabling ftp on NMC
Using ftp to put
apc_hw21_su_2-5-4-4.nmc3
onto the ON-1571 NMC. After rebooting the NMC, I was then able to successfully run the v2.5.4.4 Firmware Update Utility. The key is that this model ON-1571 NMC is only compatible with _su_ firmware. I had tried to upgrade to a _sucan_ version and that's what caused the corruption initially.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of