Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Problem with Powerchute powering down machines (VMware Vcenter 6.0.0)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problem with Powerchute powering down machines (VMware Vcenter 6.0.0)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ratatapa_apc
ratatapa_apc
Cadet

Posted: ‎2021-07-08 12:38 AM

0 Likes
1
323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:38 AM

Problem with Powerchute powering down machines (VMware Vcenter 6.0.0)

This was originally posted on APC forums on 5/22/2015


Hello everyone first post here, and please excuse my typing english is not my first language, but I will try my best to explain my problem

I have 2 UPS   let's call them UPS A and UPS B

Both are UPS  : Smart-UPS X 1500   firrmware  : UPS 09.1 (ID20)

and their NMC AP9631 Firmware :  v6.1.1  ( I think)

The UPS are Redudant which means that each server have 2 Power supply  : one that goes in UPS A and 1 in UPS B

I also have powerchute network shutdown 4.0.0 installed on a different windows machine (Physical)

I have a server let's call it ServerA, that is installed with ESXI 6.0.0.  

On that physical server I also have Vcenter 6.0.0

I have configured Powerchute to connect to the Vcenter (that is installed in a VM on server A) with the good username and password and it works because I am able to see my VMWARE host in the powerchute host protection section.  I also have the Vcenter plugin configured, and I can access powerchute directly from the Vcenter menu.

My Powerchut is also configured to talk to both UPS (with good username and password and special phrase) and I can see the 2 UPS events in the powerchute event log.

My problem is I have no idea how to correctly configure my UPS and powerchute and vmware to ask powerchute to gracefully powerdown all VM then then physical host when the battery exemple arrives at 50%  (the UPS have about 45min when battery is full so for 50% I would like the powerchut to tell the VMs then the host to gracefully shutdown after 22 minutes of no input power on the UPS)

On the VCenter I do not have the  Startup/shutdown VM section activated, but I have it on my Powerchute

Also my 2 VMs on that server atm do not have VMware tools installed (I dunno if it can change anything)

Here is the info I can give you that I have atm

In the configured events of powerchute I have not touched anything there (so all is default)

In the Virtual Machine Shutdown section of powerchute  I have the option checked with 120sec duration, and I have the VMstartup also checked at 120seconds.

I then have the Vcenter shutdown duration at 240seconds

In the UPS shutdown section (Btw I really don't understand must of APC way to explain stuff)

Low Battery duration is at 5 minutes

Basic low battery shutdown is check

Basic Low battery shutdown duration is at 30seconds.

So the test I did was unplug my UPS, and the battery dropped to like 3minutes, when the battery arrived at 5minutes the UPS started beeping without stopping, but still not VM shutdown, action on the Vcenter, and nothing in the powerchute logs to say that it tried to shutdown the machines.

So once again what I would need to do this this

1) When both UPS batteries hit 50% I want Powerchute to tell the VMs to gracefully shutdown, and then the VMwarehost to shutdown.

2) When power is back on, the powerchute restart the VMs.

Thanks and sorry for the long post, I hope people will understand my goal

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns
  • PowerChute
  • shutdown
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:38 AM

0 Likes
0
323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:38 AM

This reply was originally posted by Bill on APC forums on 5/26/2015


 

First, you must install VMware tools on each of the VM to allow them to be powered down properly. Without VMware tools install the VMs will be shutdown hard when the host is powered off.

Second, in PowerChute you can configure runtime remaining below threshold so that when the UPS battery falls below 22 minutes of runtime PowerChute will start a shutdown. The other option is to set PowerChute to start a shutdown after the UPS has been on battery for 22 minutes.

Application note 180 discusses your configuration on pages 3 and 4. Also, you should create a local account that PowerChute, vCenter, and the VMs use to communicate to ensure that the hosts and VMs are powered down properly. You will find information on creating local account starting on page 16 of the application note and in knowledge base document FA241010

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:38 AM

0 Likes
0
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:38 AM

This reply was originally posted by Bill on APC forums on 5/26/2015


 

First, you must install VMware tools on each of the VM to allow them to be powered down properly. Without VMware tools install the VMs will be shutdown hard when the host is powered off.

Second, in PowerChute you can configure runtime remaining below threshold so that when the UPS battery falls below 22 minutes of runtime PowerChute will start a shutdown. The other option is to set PowerChute to start a shutdown after the UPS has been on battery for 22 minutes.

Application note 180 discusses your configuration on pages 3 and 4. Also, you should create a local account that PowerChute, vCenter, and the VMs use to communicate to ensure that the hosts and VMs are powered down properly. You will find information on creating local account starting on page 16 of the application note and in knowledge base document FA241010

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc