Powerchute and physcal servers

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
jagagnon_apc
Cadet
0 Likes
3
346

Powerchute and physcal servers

This was originally posted on APC forums on 5/9/2016


Hello,

Does network shutdown allow managing of physical servers connected to the APC? I have configured it to shutdown my VM but I don't see anyplace in Network Shutdown to specify physical servers. 

thanks,


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
347

Re: Powerchute and physcal servers

This reply was originally posted by Bill on APC forums on 5/10/2016


Jason,

PowerChute will shutdown the Windows server it is running on after commanding the VMs and host down. Any of the other system powered by the UPS should also have PowerChute installed on it to shut those systems down. 

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
347

Re: Powerchute and physcal servers

This reply was originally posted by Bill on APC forums on 5/9/2016


Jason,

What is the operating system and how is PowerChute installed? Is the OS VMware ESXi or Microsoft Hyper-V? If ESXi is PowerChute installed on standalone Windows system, as Appliance, or on VMware vMA? Also, if ESXi is vCenter Server in use? If the OS in Hyper-V is SCVMM in use? 

jagagnon_apc
Cadet
0 Likes
0
347

Re: Powerchute and physcal servers

This was originally posted on APC forums on 5/10/2016


Hello Bill,

We installed it on a standalone windows server which is also the vcenter server. we configured it to see all hosts and shutdown as needed. There are also physical machines attached to the UPS. When a shutdown occurs will the UPS shutdown them gracefully as well or is there additional configuration needed?

thanks

BillP
Administrator Administrator
Administrator
0 Likes
0
348

Re: Powerchute and physcal servers

This reply was originally posted by Bill on APC forums on 5/10/2016


Jason,

PowerChute will shutdown the Windows server it is running on after commanding the VMs and host down. Any of the other system powered by the UPS should also have PowerChute installed on it to shut those systems down.