Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Personal Edition and runtime estimate

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Personal Edition and runtime estimate
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
andyross_apc
Ensign andyross_apc
Ensign

Posted: ‎2021-07-08 01:02 AM

0 Likes
5
600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:02 AM

Personal Edition and runtime estimate

This was originally posted on APC forums on 7/12/2015


I installed Powerchute Personal Edition 3.02 a week or so ago. I've had the UPS for quite awhile, but just used the basic 'treat it like a laptop battery' of Windows 7. I installed it as I wanted to check a few things after a long outage drained the battery. It's a Back-UPS ES750, and the battery is only 10 months old. It took a few days for it to reach 100%.

So far, the estimated runtime bounces between 1 and 2 minutes. It shows I'm using around 108-115 Watts, out of 450. I have run a self-test, which passes. How long does it take to get a realistic estimate? Do I need to deliberately run it off the battery for awhile?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • edition
  • personal
  • PowerChute
  • runtime
  • windows
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:02 AM

0 Likes
0
603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:02 AM

This reply was originally posted by Bill on APC forums on 7/27/2015


Andrew,

The battery should be able to sustain the load for 20 plus minutes. I recommend you call into Technical Support 1-800-890-4272 since the battery is under warrant.

As for the battery manufacturer, we have a few manufactures that are approved to supply batteries. The all meet the same quality standards.

See Answer In Context

Reply
Share
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:02 AM

0 Likes
0
603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:02 AM

This reply was originally posted by Bill on APC forums on 7/13/2015


Andrew,

Switch the UPS to battery output with the computer attached should give you an accurate reading.

Reply
Share
andyross_apc
Ensign andyross_apc
Ensign

Posted: ‎2021-07-08 01:02 AM

0 Likes
0
603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:02 AM

This was originally posted on APC forums on 7/13/2015


I wonder if the battery is bad, or something needs to be 'reset' to relearn the battery. I unplugged the UPS with the monitor running, and it was dropping very fast. It was down to 73% and the UPS started continuously beeping in barely 30 seconds. The battery is a genuine APC that is only 10 months old...

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:02 AM

0 Likes
0
603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:02 AM

This reply was originally posted by Bill on APC forums on 7/14/2015


Andrew,

Sounds like a bad battery. You should contact Technical Support at 1-800-890-4272. Since the battery is only 10 month old it is under warranty and can be replaced.

Reply
Share
andyross_apc
Ensign andyross_apc
Ensign

Posted: ‎2021-07-08 01:02 AM

0 Likes
0
603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:02 AM

This was originally posted on APC forums on 7/25/2015


I bought a brand new battery. Gave it a few days to guarantee it's fully charged. I then did a pull-the-plug test. And just like the previous battery, the percentage available dropped very fast, and the UPS started continuously beeping after less than a minute. Just how long should a 120W load run? Or is it the cheap Made-In-Vietnam battery (I peeled back the APC label) you are now shipping as official APC batteries? The original battery that came with the UPS when I bought it a few years ago was a CSB brand.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:02 AM

0 Likes
0
604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:02 AM

This reply was originally posted by Bill on APC forums on 7/27/2015


Andrew,

The battery should be able to sustain the load for 20 plus minutes. I recommend you call into Technical Support 1-800-890-4272 since the battery is under warrant.

As for the battery manufacturer, we have a few manufactures that are approved to supply batteries. The all meet the same quality standards.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc