Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

PCNS Shutdown inc VMWare

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: PCNS Shutdown inc VMWare
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Dobs-tr_apc
Ensign Dobs-tr_apc
Ensign

Posted: ‎2021-06-30 08:32 AM

0 Likes
2
191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:32 AM

PCNS Shutdown inc VMWare

This was originally posted on APC forums on 6/2/2009


I have installed PCNS on all of our physical servers and all the guests on our ESX 3.5 server. Each physical server has a dual PSU which is connected into seperate PDU's which in tern are connected to one of the 2 Smart UPS 3000's with AP9619 Network management Cards installed.

I have set levels for the critical temperatures etc and the low battery duration each on these UPS's

I will also install the PCNS for VMWare on our ESX Server.

I have noticed the "Turn off the UPS after the shutdown finishes" tick box is selected on all the PCNS clients.

Is the way the system works that the Network Management cards will turn off the UPS once ALL the PCNS clients have shutdown including the client installed on the VMWare ESX 3.5 server? I'm hoping it won’t turn the whole UPS off once the first server shuts down!

Also how do I specify the ESX server to start to shutdown AFTER all its guests have? This would apply to a power failure and the temperature going over the critical limit.

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Dobs-tr_apc
Ensign Dobs-tr_apc
Ensign

Posted: ‎2021-06-30 08:32 AM

0 Likes
0
191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:32 AM

This was originally posted on APC forums on 6/3/2009


excellent thanks very much

See Answer In Context

Reply
Share
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:32 AM

0 Likes
0
191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:32 AM

This reply was originally posted by Angela on APC forums on 6/2/2009


you need to do a couple of things.

"Turn off the UPS after the shutdown finishes" should be ONLY checked on the last PCNS client to shutdown, so presumably the barebones ESX server itself.

also, for help in getting the Guest OSs to shutdown you can either install PCNS on them like a normal machine, if they are bridged to the same network as the management card (which it sounds like this is what you were doing), or install VMWare tools and use that.

[here is a VMWare knowledge base article to help you out|http://kb.vmware.com/selfservice/microsites/search.do?language=en_US&cmd=displayKC&externalId=100818...]

if you install PCNS on the Guest OSs and go that route, you can configure the UPS: On Battery event for example to shutdown the particular Guest OSs and then make the ESX server shutdown based on the low battery duration of the network management card.

The low battery duration in the network management card is the setting that when reached, so for example say its set to 5 minutes, that when there is 5 minutes of runtime remaining on the UPS, it will force everything to shutdown if it wasnt configured with a special shutdown setting based on a certain event.

hope this helps!

Reply
Share
Dobs-tr_apc
Ensign Dobs-tr_apc
Ensign

Posted: ‎2021-06-30 08:32 AM

0 Likes
0
192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:32 AM

This was originally posted on APC forums on 6/3/2009


excellent thanks very much

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc