We had a few problems to configure our NMC3 and USV with PCNS for a single Server and a few network devices.
Here is what we did yesterday
A single Dell R760 Server is connected to Outlet Group 1 with Power Supply 1 and Power Supply 2.
1 CISCO Switch (Passiv), a FortiSwitch (Passiv) and a Fortigate (Passiv HA) are connected to Outlet Group 1.
1 CISCO Switch (Active), a FortiSwitch (Active) and a Fortigate (Active HA) are connected to Main Outlet Group.
PCNS / Dell Server has configured Events
- If Runtime exceeds with a Delay of 0 Second. I can´t set any Duration (for shutdown) in PCNS 5.2
- So the Server would shutdown as soon as the USV has a Runtime exceeds (30min)
- I have not configure "Do not turn off the UPS" in PCNS
NMC3 - Shutdown
NMC3 - Main: Unswitched Group
NMC3 - Outlet Group 1
Now we started testing.
We pulled the mains power supply for USV.
PCNS started a shutdown 60 seconds later and the Dell Server was powered off.
Outlet Group 1 was still alive even after 7-8 minutes (Switches on Group 1 where still alive).
Main Unswitched Group was still alive even after a couple of minutes (Switches on Main Group where still alive).
I know, when i trigger a manual outlet group action , i can see a timer for the outlet groups counting down.
Q1: Is there any counter visible for the Main or Group 1?
Our Goal is this.
If power is lost and runtime exceeds, Dell Server should shut down after a delay of 0s.
PCNS controls the UPS and should not Turn of Group 1.
Q2: Will tis trigger only Group 1 AND Main Group shutdown?
Q3: Is the Main Group triggered after Group 1 or is triggerd after Group 1 is turned off (staged)?
Now a few questions
What will happen, if the Server is already shutdown (but still has power on PSU 1/2),
Group 1 is not turned off (delay timer is at 40 seconds) and main group is not triggered yet AND the power returns?
Q4: Will the timer for Group 1 stop and the outlets are still of OR will they get a power cylce.
The dell server needs a power cycle to power on.
Q5: If the main timer started and is at 40 seconds AND power returns, will the main group power cycle OR is nothing done?
Now we had a strange error and the USV doesn´t restarted at all.
Because the server was offline and the battery showed a runtime of 25 min, we connected a small elctic radiator.
USV jumped down to 3 minutes remaining, beeped load and showed this log entry.
"UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107"
Q6: The Group 1 and Main Group did not power off at all (we checked the logs)?
After a another 2 mins, the USV was silent and only the display showed some information.
One info showed, the battery is at 0% and no AC input is deteted.
All LED´s on the display where cycline (4 LED with different color).
After returning the mains power, the USV was not respondig at all.
It did not come up againg, even after 10 minutes, it was still not charging the battery.
I needed to press the powerbutton , i am not shure yet, but i think i checked the information and menu.
And after dis/reconnection mains again and pressing ON button, the USV was comming up.
Q7: Why did the USV doesn´t come up properly or shutdown properly at all.
Can someone help in this setup
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-07 12:33 AM
Where are all the APC / NCM Experts?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-08 05:16 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-13 05:04 AM
Thanks for your reply, i will try theses settings.
But it's sad that even after four weeks, APC Support still can't provide any answer.
Schneider Support can't provide any answers either;
the only thing they managed to do was delete my ticket (126865013) from the Schneider ticket system without any comment.
A real disgrace