Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Outlet Group behavior AND USV trouble shooting

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Outlet Group behavior AND USV trouble shooting
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5060
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
JuergenB
JuergenB
Explorer

Posted: ‎2026-09-04 01:58 AM

0 Likes
3
356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-04 01:58 AM

Outlet Group behavior AND USV trouble shooting

We had a few problems to configure our NMC3 and USV with PCNS for a single Server and a few network devices.

 

  • APC USV - SLT3000RMI2UC (FW UPS 18.0 (ID1015))
  • APC NMC3 - AP9641 (APC OS v3.4.1.4)
  • APC PCNS - Release 5.2.0

Here is what we did yesterday

 

A single Dell R760 Server is connected to Outlet Group 1 with Power Supply 1 and Power Supply 2.
1 CISCO Switch (Passiv), a FortiSwitch (Passiv) and a Fortigate (Passiv HA) are connected to Outlet Group 1.
1 CISCO Switch (Active), a FortiSwitch (Active) and a Fortigate (Active HA) are connected to Main Outlet Group.

 

PCNS / Dell Server has configured Events

- If Runtime exceeds with a Delay of 0 Second. I can´t set any Duration (for shutdown) in PCNS 5.2
- So the Server would shutdown as soon as the USV has a Runtime exceeds (30min)
- I have not configure "Do not turn off the UPS" in PCNS

 

NMC3 - Shutdown

  • Low Battery Duration 30min
  • Basic Low Battery Duration 120sec
  • Sleep Time 0.2h
  • Max Required Delay / Force negotionen (not selected)
  • On-Battery Shutdown Behavio / Restart when power is restored (selected)
  • Turn off and stay off (not selected)
  • Ignore PCNS shutdown commands (not selected)

NMC3 - Main: Unswitched Group

  • Power Off Delay - 300s
  • Reboot Duration - 60s
  • Power On Delay - 60s
  • Min Return Runtime - 60s
  • Load Shedding
  • Turn Off Outlet Group when:
  • power failure lasts longer than (not seleceted)
  • UPS runtime remaining is less than (not seleceted)
  • Skip outlet off delay Skip outlet off delay (not seleceted)
  • Stay off after power returns seleceted (not seleceted)

NMC3 - Outlet Group 1

  • Power Off Delay - 300s
  • Reboot Duration - 60s
  • Power On Delay - 60s
  • Min Return Runtime - 60s
  • Load Shedding
  • Turn Off Outlet Group when:
  • power failure lasts longer than (not seleceted)
  • UPS runtime remaining is less than (not seleceted)
  • UPS is overloaded (not seleceted)
  • Skip outlet off delay Skip outlet off delay (not seleceted)
  • Stay off after power returns seleceted (not seleceted)

Now we started testing.

 

We pulled the mains power supply for USV.

PCNS started a shutdown 60 seconds later and the Dell Server was powered off.
Outlet Group 1 was still alive even after 7-8 minutes (Switches on Group 1 where still alive).
Main Unswitched Group was still alive even after a couple of minutes (Switches on Main Group where still alive).

 

I know, when i trigger a manual outlet group action , i can see a timer for the outlet groups counting down.


Q1: Is there any counter visible for the Main or Group 1?

 

Our Goal is this.

If power is lost and runtime exceeds, Dell Server should shut down after a delay of 0s.
PCNS controls the UPS and should not Turn of Group 1.

 

Q2: Will tis trigger only Group 1 AND Main Group shutdown?
Q3: Is the Main Group triggered after Group 1 or is triggerd after Group 1 is turned off (staged)?

Now a few questions

 

What will happen, if the Server is already shutdown (but still has power on PSU 1/2),
Group 1 is not turned off (delay timer is at 40 seconds) and main group is not triggered yet AND the power returns?

 

Q4: Will the timer for Group 1 stop and the outlets are still of OR will they get a power cylce.
The dell server needs a power cycle to power on.

Q5: If the main timer started and is at 40 seconds AND power returns, will the main group power cycle OR is nothing done?

 

Now we had a strange error and the USV doesn´t restarted at all.
Because the server was offline and the battery showed a runtime of 25 min, we connected a small elctic radiator.


USV jumped down to 3 minutes remaining, beeped load and showed this log entry.

 

"UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107"

 

Q6: The Group 1 and Main Group did not power off at all (we checked the logs)?

 

After a another 2 mins, the USV was silent and only the display showed some information.
One info showed, the battery is at 0% and no AC input is deteted.

All LED´s on the display where cycline (4 LED with different color).
After returning the mains power, the USV was not respondig at all.
It did not come up againg, even after 10 minutes, it was still not charging the battery.

I needed to press the powerbutton , i am not shure yet, but i think i checked the information and menu.
And after dis/reconnection mains again and pressing ON button, the USV was comming up.

 

Q7: Why did the USV doesn´t come up properly or shutdown properly at all.

 

Can someone help in this setup

 

Thanks

Labels
  • Labels:
  • Datacenter UPS
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
JuergenB
JuergenB
Explorer

Posted: ‎2026-10-07 12:33 AM

0 Likes
0
271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-07 12:33 AM

Where are all the APC / NCM Experts?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2026-10-08 05:16 AM

0 Likes
0
255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-08 05:16 AM

If you configure UPS to turn off in PowerChute, PowerChute will command the outlet groups to shut off when a shutdown is triggered. Based on your settings, outlet group 1 will wait 300 seconds, then cut output. The main will not power off until group 1 has powered off; once group 1 has powered off, the main will wait 300 seconds and cut output. 
 
When the server and UPS shutdown is triggered, and AC is restored before the server and UPS power off, the systems will continue to power off. Once both outlet groups have cut AC output, when street AC is restored, the UPS will wait until the UPS runtime is 60 seconds, then the power-on delay of 60 seconds, and the main outlet group will restore AC output. Once the main outlet group is on, group 1 will wait 60 seconds and restore output.  
If the UPS does not cut output, review the PCNS event log to verify the command was sent, and the UPS replied, "Outlet group turn off initiated."
Example:
 
10/08/2026  07:31:44    Shutdown process started. Linux will shut down soon. 
10/08/2026  07:31:44    PowerChute is turning off UPS 192.168.0.166     
10/08/2026  07:31:52    UPS Outlet Group: Outlet Group 1 turn off has been initiated.  
10/08/2026  07:31:52    UPS critical event: <b>Outlet Group Turn off initiated</b>.
 
If you see the entry, PowerChute is turning off the UPS but don't see the NMC reply, reboot the NMC and rerun the shutdown test. 
If you don't see the entry "PowerChute is turning off UPS," verify that PCNS is configured to turn the UPS off.
 
BillP_1-1791461646953.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JuergenB
JuergenB
Explorer

Posted: ‎2026-10-13 05:04 AM

0 Likes
0
176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-13 05:04 AM

Thanks for your reply, i will try theses settings.

 

But it's sad that even after four weeks, APC Support still can't provide any answer.
Schneider Support can't provide any answers either;
the only thing they managed to do was delete my ticket (126865013) from the Schneider ticket system without any comment.

A real disgrace

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore