Minimal modules configuration to start a Symmetra PX2.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Minimal modules configuration to start a Symmetra PX2.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Roio
Crewman Roio
Crewman

Posted: ‎2022-09-19 04:33 PM

0 Likes
1
676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-19 04:33 PM

Minimal modules configuration to start a Symmetra PX2.

Hello, we have a malfunctioning Symmetra PX2. This has gone through several technicians but they haven't been able to diagnose the problem. I think there must be some problem in the communication bus, since apparently the individual modules seem to work.

Currently I am trying to power it with the least number of modules, a power module, a battery pack without and whithin the communication module, a single inteligence module (MIM) or both (MIM/RIM) and the static switch.

I really don't know how to continue with the UPS power on. It currently does not detect any power modules.

The LCD screen does not respond to the commands sent by the keyboard and the alarms are not updated.

But the following information could be obtained via an extra network card.

 

"No Power Modules Detected"

"Extended Run Frame Fault"

"Output power Turned Off"

"System Start-Up Configuration Fault"


MIM: R State; 00 000 0000 1000 00401 000 1E 0000
RIM: R State; 00 000 0000 1000 00401 000 1E 0000

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
sesa298777
Crewman sesa298777 Crewman
Crewman

Posted: ‎2022-10-05 08:52 AM

0 Likes
0
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-05 08:52 AM

Hi,

 

What age is your UPS? Could you provide the two letters and first four digits of the serial number? This will indicate the week and year of manufacture.

What is the UPS model number?

Has it ever worked in its current location?

The Symmetra PX is a complex unit. I would suggest it better to create a case and get one to one assistance from Technical Support.

If you go to APC.com and select your country.

Select “Support” and contact us.

If you use “Use our web form” and submit your question now. You will have the ability to complete a web form with your UPS details and your contact detail. This when submitted will go to the correct team.

 

Kindest Regards,

Rich...

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of