Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Is it possible to power-limit a Galaxy VS 50 kW UPS to operate safely on a 30 kW electrical infrastructure?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is it possible to power-limit a Galaxy VS 50 kW UPS to operate safely on a 30 kW electrical infrastructure?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
160
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Gregory_Jimenez
Gregory_Jimenez
Explorer

Posted: ‎2026-07-01 07:16 PM

0 Likes
1
91
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-01 07:16 PM

Is it possible to power-limit a Galaxy VS 50 kW UPS to operate safely on a 30 kW electrical infrastructure?

 

Hello everyone,

I am looking for some technical advice or possible workarounds regarding an installation issue with a Galaxy VS UPS.

The Context: We originally quoted and ordered a 30 kW Galaxy VS UPS (GVSUPS30KB4GS). However, due to a shipping error, we received the 50 kW model (GVSUPS50KB4GS).

The Problem: The electrical infrastructure at the site—including piping, AWG wiring, and 60A breakers—is already fully installed and dimensioned specifically for the maximum input current of the 30 kW unit. According to the installation manual, the 50 kW UPS requires 100A breakers and a larger wire gauge (AWG 3/2).

It is important to note that the actual critical load connected to the UPS will remain exactly the same as originally planned, well within the 30 kW capacity.

My Question: Is there any official way to configure, power-limit, or restrict the 50 kW UPS via software/firmware (for example, limiting the battery charging current or capping the maximum input power) so that it can safely operate on the existing 60A infrastructure without risking tripping the breaker?

Replacing the UPS entirely (waiting for the correct 30 kW model) or replacing the newly installed wiring and breakers would cause a considerable delay and severely impact the end customer's timeline.

Has anyone faced a similar situation or can confirm if Schneider Electric supports a software-level limitation for this scenario?

Thank you in advance for your support and technical guidance.

Image preview.png

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Teken
Champion

Posted: ‎2026-07-02 03:50 AM

0 Likes
0
79
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-02 03:50 AM

Code would dictate that everything must match from supply, protection, to connected load.

 

If we ignore the above for a moment the reality is this is like any high output device. You can have a very powerful generator but nothing impacts you from using less power than the unit can provide and sustain.

 

If everything is taken at face value as to the current installation the breaker will trip and never allow you to draw more than 60 amps from the service panel.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.