New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Is it possible to power-limit a Galaxy VS 50 kW UPS to operate safely on a 30 kW electrical infrastructure?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-07-0107:16 PM
Is it possible to power-limit a Galaxy VS 50 kW UPS to operate safely on a 30 kW electrical infrastructure?
Hello everyone,
I am looking for some technical advice or possible workarounds regarding an installation issue with a Galaxy VS UPS.
The Context: We originally quoted and ordered a 30 kW Galaxy VS UPS (GVSUPS30KB4GS). However, due to a shipping error, we received the 50 kW model (GVSUPS50KB4GS).
The Problem: The electrical infrastructure at the site—including piping, AWG wiring, and 60A breakers—is already fully installed and dimensioned specifically for the maximum input current of the 30 kW unit. According to the installation manual, the 50 kW UPS requires 100A breakers and a larger wire gauge (AWG 3/2).
It is important to note that the actual critical load connected to the UPS will remain exactly the same as originally planned, well within the 30 kW capacity.
My Question: Is there any official way to configure, power-limit, or restrict the 50 kW UPS via software/firmware (for example, limiting the battery charging current or capping the maximum input power) so that it can safely operate on the existing 60A infrastructure without risking tripping the breaker?
Replacing the UPS entirely (waiting for the correct 30 kW model) or replacing the newly installed wiring and breakers would cause a considerable delay and severely impact the end customer's timeline.
Has anyone faced a similar situation or can confirm if Schneider Electric supports a software-level limitation for this scenario?
Thank you in advance for your support and technical guidance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-07-0203:50 AM
Code would dictate that everything must match from supply, protection, to connected load.
If we ignore the above for a moment the reality is this is like any high output device. You can have a very powerful generator but nothing impacts you from using less power than the unit can provide and sustain.
If everything is taken at face value as to the current installation the breaker will trip and never allow you to draw more than 60 amps from the service panel.