Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Interaction of Cool Setpoint and Supply Air Setpoint in Inrow environment (i. e. ACRC103)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Interaction of Cool Setpoint and Supply Air Setpoint in Inrow environment (i. e. ACRC103)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
LALM
Crewman LALM
Crewman

Posted: ‎2022-01-26 08:05 AM

0 Likes
8
2305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-26 08:05 AM

Interaction of Cool Setpoint and Supply Air Setpoint in Inrow environment (i. e. ACRC103)

Hello world,

 

I am trying to understand the control mechanism of InRows operating in Inrow environment (open & common cold aisle). Maybe one of you can help me?

 

First, let's begin with InRows programmed for HACS (Hot Aisle Containment System) environment. Relevant settings are Supply Air Set Point and Fan Speed Preference. While the Supply Air Set Point is determining the temperature of the air leaving the cooling unit, the Fan Speed Preference is defining the maximum delta of temperature between supply air and return air. In other words: the fan speed will only increase once the return air temperature would otherwise exceed the Supply Air Set Point plus the Fan Speed Preference.

 

Now, coming to InRows programmed for Inrow environment. Relevant settings are Supply Air Set Point and Cool Set Point. While the Supply Air Set Point is still determining the temperature of the air leaving the cooling unit, the Cool Set Point is the temperature the cooling group should maintain (so Supply Air Set Point must always be lower then the Cool Set Point). The fan speed is controlled by comparing the rack inlet temperature to the cooling setpoint. If the rack inlet temperature increases compared to the Cool Set Point the fans increase output to maintain the setpoint. If the rack inlet temperature decreases compared to the Cool Set Point the fans decrease output to maintain the setpoint. Up until this point all seems still fine to me. However, since the rack inlet temperature is representing the air entering the rack, it should be nearly identical to the supply air leaving the cooling unit. If the Supply Air Set Point is set to for example 20 °C and the Cool Set Point to 24 °C, does it mean that the fan speed would stay at minimum speed up until the cold water valve in the InRow opened up to 100% and the actual supply air starts to deviate from the setpoint increasing to 24 °C until it matches the Cool Set Point? Also, what would be typical / appropriate delta between those to setpoints?

 

Thanks in advance for clearing this up for me!

Labels
  • Labels:
  • Datacenter Racks & Cooling
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-01-28 08:26 AM

0 Likes
7
2280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-28 08:26 AM

Hello and thank you for your question.

 

Regarding your query what if the Cool Setpoint was set higher than Supply setpoint we would just like to state that the Supply Air setting is defined by Schneider Electric authorized personnel only when the cooling unit or group of units are commissioned. We do not recommend that the Supply Air setpoint is ever set higher than the Cool setpoint.

 

Regarding your query “what would be typical / appropriate delta between those to setpoints?”

We recommend that the Cool setpoint is a minimum of 0.50C greater than the Supply Air setpoint.

 

Also, please see below some information regarding the control operation of the InRow RC units:

 

The InRow RC continually adjusts its cooling output to accommodate varying loads. The cooling output is determined by the difference between the supply air temperature setpoint and the actual supply air temperature as well as the airflow (for each of the cooling units in the cooling group if more than one cooling unit is present).

 

In-row (open aisle) mode

 

The In-row (open aisle) mode is characterized by the free circulation of air, quantified by mf (mass flow) and T (temperature). The IT equipment draws in cool air from the cold aisle and rejects it to the hot aisle. The CRAC takes hot air from the hot aisle and supplies cool air to the cold aisle. There may be mixing of the cold and hot aisles over the top of the racks, around the sides, etc.

 

InRow RC Airflow Management

Changes in fan speed are always limited to a maximum of 2% per second. This limitation prevents the unit airflow from changing too quickly when the operating mode or active environmental control function changes, thereby improving control stability.

 

InRow RC-CW Cooling Control

The supply temperature controller regulates the chilled water (CW) valve and is responsible for maintaining the leaving air temperature at the desired set point. This works identically for InRow, HACS, and RACS. Minimum valve position is where there is essentially no flow through the coil. By preventing the valve from closing entirely while in operation, the unit can be more responsive to increases in heat load. The valves’ maximum position is where there is no additional flow through the coil. By limiting the maximum position, the controls can respond faster to a drop in the heat load.

 

 

Fan control

In the graph, illustrated above, the mass airflow is determined by T (remote), which is the maximum reading of the unit’s three Remote Temperature Sensors. The minimum fan speed is 30%. This speed was chosen to prevent fan bearing wear, and to ensure that there is always some airflow over the temperature sensors so that readings are accurate.

 

Supply air temperature control

The chilled water valve is controlled by the supply temperature controller which is responsible for maintaining the leaving air temperature at the desired set point. The controller’s input is the leaving air temperature T supply, measured by the integral supply temperature sensor, and its output is a commanded CW valve position. The design of the supply temperature controller is the same for all rack configurations.

 

InRow RC Group Cooling Control

Supply air temperature control

Each unit controls their chilled water valve (RC-CW) independently based on their own supply temperature sensor reading. In a group configuration the supply temperature setpoint is shared among all the units, with each unit managing its own chilled water valve or compressor based on its own supply temperature. Thus, there is no need for group control of the supply temperature.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-01-28 08:27 AM

In response to CiaranR
0 Likes
6
2278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-28 08:27 AM

Capture.PNGCapture2.PNG

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LALM
Crewman LALM
Crewman

Posted: ‎2022-02-04 04:53 AM

In response to CiaranR
0 Likes
5
2228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-04 04:53 AM

Thank you @CiaranR for your very elaborate answer! Now there is only one question left on my side. In section 'Fan Control' you speak of three remote temperature sensors. As far as I know our units have three temperature sensors: 1 each for supply air, rack inlet and return air. Are those the ones you speak of? If that's the case, will the latter not always be the maximum reading (assuming no major screw ups happen to mix air between hot and cold aisle significantly)?

 

Have a great weekend!

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-02-10 06:37 AM

In response to LALM
0 Likes
4
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-10 06:37 AM

Hi LALM,

 

Yes, the three sensors I was referring to are the Supply air, Return air and Rack inlet sensors. To be clear I was referring to the air temperature sensors specifically as there are also fluid sensing temperature probes. However, technically only one is "remote"...the rack inlet temperature sensor. The remote temperature sensor comes coiled inside the equipment and must be mounted on a rack server inlet, or the equipment will not operate properly. The remote temperature sensor monitors the room temperature, monitoring the environment surrounding the cooling equipment to ensure that the conditioned air is cooling the area.

With regards to your question "will the latter (return air sensor I assume?) not always be the maximum reading (assuming no major screw ups happen to mix air between hot and cold aisle significantly)?

 

The answer is yes, in theory the Return air temp should always be the maximum reading as it is monitoring the air temp on the warm side of the evaporator coil prior to any cooling has been performed.

 

  • Supply Air: The air output from the cooling unit. The average temperature of the air leaving the cooling unit, as measured by the upper and lower supply air temperature sensors.
  • Return Air: The air entering the cooling unit. The average temperature of the air entering the cooling unit, as measured by the upper and lower return air temperature sensors.
  • Rack Inlet (Remote Temperature Sensor): The air entering the server rack at the temperature sensor.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-02-10 06:38 AM

In response to CiaranR
0 Likes
3
2192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-10 06:38 AM

 
Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-02-10 06:39 AM

In response to CiaranR
0 Likes
2
2190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-10 06:39 AM

 

Capture.PNG

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LALM
Crewman LALM
Crewman

Posted: ‎2022-03-02 07:53 AM

In response to CiaranR
0 Likes
1
2134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-02 07:53 AM

Hey @CiaranR,

 

what would happen if one would choose in-row (open aisle) mode in an actual hot aisle containment system environment and thus,  there should be no (significant) potential of warm and cool air actually mixing? Reasons for wanting to operate the InRows in in-row mode instead of HACS would be a low IT load inside a room, leading to the units never running above minimum fan speed, which for the model in use is different for HACS (50%) and in-row (30%) mode (energy saving potentials). How to set the set points properly?

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CiaranR
Ensign CiaranR Ensign
Ensign

Posted: ‎2022-03-04 06:42 AM

In response to LALM
0 Likes
0
2127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-04 06:42 AM

Hi @LALM 

 

The short answer is I have no idea what the outcome would be in such a scenario as I have not encountered this before however, if it is a low thermal load which is concerning you then there is always the option of placing a number of units on Standby mode (dependent on the number of units installed vs the load). Note: Newer units have a “Load Assist” and “Runtime Balancing” functionality to address such a situation.


To hazard a guess however I can see no reason to suggest that this would not be a successful strategy as in an InRow environment, the cooling unit supplies constant-temperature supply air to the common cold aisle. The fan speed is modulated to ensure that the desired volume of air reaches the IT equipment. The fan speed is determined by the difference between the cooling setpoint and the maximum rack air inlet temperature. In a HACS environment, the cooling unit neutralizes the heat accumulated in the common hot aisle and expels it back into the surrounding environmental space while maintaining the desired temperature in the cold aisle.


I wish to note also that switching to InRow mode from HACS to make energy savings based upon the lower fan speed may inadvertently cause excessive condensation. The condensate pumps in these units are relatively small and are not designed to handle significant amounts of water.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc