New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Identify batteries to be replaced
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-07-3009:08 AM
Identify batteries to be replaced
Hi.
If i have an UPS with an extra battery module, and the device has Battery Replacement Needed alarm, how i can identify which battery need to be replaced. It is the internal UPS battery or the batteries of the extra module.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-07-3102:23 PM
LCD Menu: Go to Status -> Battery: As you scroll through the menu the system will indicate the current battery health, temperature. If there's a problem a message will be displayed for that specific (RBC) Replacement Battery Cartridge.
All of the latest generation of SRT incorporates a Status LED behind the front bezel. It will flash to indicate if there is an active fault / problem.
NMC: Log into the NMC internal website and go to Status -> Battery System: All listed and connected RBC and extended battery packs will be displayed. The system will display the Health & Status at a glance. Selecting any of the links will display the health, status, temperature, installation date.
You may use either method to identify which RBC needs to be replaced.