Firmware Update of AP8841

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
473

Firmware Update of AP8841

This question was originally posted by Matthew on APC forums on 3/31/2020


We have a very out of date firmware of 5.1.6 and I'm trying to update it. When I open the Windows upgrade utility and put in all the required information, it says the FTP login is invalid. It pings successfully and I can log into the web interface with the admin account.

1) Is it ALWAYS apc/apc for FTP login?

2) if it isn't, is there a way to reset it?

Unfortunately our data center guy no longer works with us and he took care of all of this. Thanks all.

Tags (3)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
473

Re: Firmware Update of AP8841

This reply was originally posted by Bill on APC forums on 4/7/2020


Hi,

Log into the PDU and go to Administration - Network - FTP and verify FTP is enabled. 

If enabled go to Administration - Security - Administrator and verify the Administrator is apc and the password is apc. 

See Answer In Context

Attachments
1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
474

Re: Firmware Update of AP8841

This reply was originally posted by Bill on APC forums on 4/7/2020


Hi,

Log into the PDU and go to Administration - Network - FTP and verify FTP is enabled. 

If enabled go to Administration - Security - Administrator and verify the Administrator is apc and the password is apc. 

Attachments