Hi,
I have some faulty Symmetra Lx Power modules type SYPM4KI. Few of them have faulty board INVERTER BD. Model 640-0476J REV 9.I will name fault as an" starting problem of Power module". When I turn UPS on, this Power module does not go ON, and display in Diagnostic position is indicating :
Power module - faulty
Row Status Dump data :0804 02A0 8000 2080 0002 0840 7C 0700 0000 59 8483 0000.
When I change mentioned INVERTER BD. with good one, Power module is working ok.
Now I am asking you guys for your comment and help to eliminate problem on this "board".
I have some questions :
- Can I buy separately boards -parts of Power module?
- How can I check INVERTER BD. to verify for correct operation( signal on test points or something similar).
-What are telling to me Row Status Dump data's and how can I decode them?
p.s.
Four days before I send " task about IM module of Symmetra Lx " but I did not have any comment or help from You ! It was my first post to forum.
Regards -Mehdi,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:07 AM . Last Modified: 2024-03-18 02:44 AM
Hi, have you been able to solve it? We have the same problem with inverter board.
Raw data:0804 02A0 8100 2000 0002 08 .....
Regards
Jiri
EDIT: We figured it out, it was one of the smd cap's.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:07 AM . Last Modified: 2024-03-18 02:44 AM
Hi, have you been able to solve it? We have the same problem with inverter board.
Raw data:0804 02A0 8100 2000 0002 08 .....
Regards
Jiri
EDIT: We figured it out, it was one of the smd cap's.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-17 11:32 AM
can you describe how you troubleshooted and replaced the caps?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-04 08:01 AM
From the communications board, inverter phase or PFC? where did you exactly did this? i would like to know where exactly did you find it, and how did you identify it? did you just did a contuinity test on the cap and found a short? or you had to desolder it and measure it with capacitance meter?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-08 12:28 AM
Good Morning
Just some help with the board Number. On every APC UPS PCB is a white sticker with a barcode and a number.
take down the first six numbers. Replace the first two numbers with "0P" followed by number 3 to 6 and you have the boards number.